It is a pain
im thinking of isolating the two earthing systems from each other, having a rod for each and insulating the SWA sheath at the house end from the barn see what happens
just wanted a few ideas for when i get back there
Ramp test the house RCD
Oppps my bad never saw post 18... lol
Ok find the location of the TX relative to the house and barn i suspect if all other scenario's are exhausted i may have an idea.
PS if it is what I suspect you get an arkward situe to address and sometimes its not easy to sort without contravening the Regs.
I don't think he has enough info yet , he needs access to that house and some test results as well,,,,
So where is the single point means of isolation to this farm installation??
Are you absolutely SURE that an earth fault in the barn is tripping the house's downstream 30mA RCD and not the other way round?
Isolating TT earthing systems, what do you think you'll achieve by doing that?? I'd be looking at more towards as to what and how these rod(s) are connected into the system. In fact each building should be roded and then physically connected together. Done properly you could well end up with a neigh on TN Ra value.
Engineer 54 wrote;
there is none!
When the flood lights to the exterior of the barn was switched on they tripped the main RCD in the barn and the isolated 30mA rcd in the house, i have removed this N-E fault but they want to sort this problem as it has happened in the past and a few electricians before me have failed to diagnose the problem, they are also two independant supplies so either way it shouldnt happen
Although i have not yet been to the house to investigate further, there was a post that was referring to fault current using the house main bonding path rather than the earth rod at the barn as there is no main bonding at the barn end as its all plastic piping , and i know that there is PME connections to local houses so that is probably the case, i was doubtful of whether this is likely to affect the house RCD, but then im a bit short on solutions
on this install i would think it fortunate if there is more than one rod lol
Engineer 54 wrote;
there is none! Then one needs to be provided then doesn't it!!
Take some photo's of this incoming arrangement and lets have a look...
Should be independent, but depends on how they have been connected, or even possibly interconnected . Farm installations are notorious for out of sight cheap that'll do DIY add-ons and obscure ancient lash-ups. So you might want to have a good walk round to see what you can find... lol!!
Isolating TT earthing systems from each other isn't going to serve any purpose whatsoever.
How far away are these other houses in relation to the farm? Unless they are on the same distribution line as the farm, it's doubtful.
Is the farmhouse connected for PME?? On a farm installation, i would personally connect a local earth rod to any and all buildings MET/EMT. Any stray currents will then have a local N-E rod path to run too. But to be effective they need to have a single to very low double figure Ra value...
As i say a few photo's wouldn't go amiss here to show exactly what you have at this farm, at the intake position and farmhouse.