Now we have the correct set-up as confirmed in my post 13 any chance the OP can answer y questions way back in post 2 :juggle2: ill just wait then!!
 
head scratcher alright, but I think I would be eliminating any N-E faults on both installations in the absence of any better ideas. N-E faults do funny things to RCD's.......
 
You need access to the house , to confirm what RCDs are there and earthing arrangements at the house,,,
 
well certainely a headscratcher alright, seems very strange, maybe the fact both supplys connect to the rod and the fact a surge to earth trips the one may mean the other is over sensitive, must admit it is a funny situation which I am struggling with at the moment.
 
You need access to the house , to confirm what RCDs are there and earthing arrangements at the house,,,


Yes i am due back there saturday
 
he said henleys, switchfuse, rcd.

then i hear TP board and TT the first thing i think of, is the first (RCD) enclosure insulated?


No the enclosures are not insulated or the dist board, its an old install and a stubborn farmer

first thing i mentioned to him
 
La de da da da ....any chance of responding to post 2 yet its getting further away as we speak... might be using the 18th edition by the time you respond to it :juggle2:

Please refer to post 21 for guidance.
 
  • Like
Reactions: 1 person
Welchyboy1 however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too any ideas?[/QUOTE said:
A strange one indeed .

first thing to do would be confirm this is actually happening with test meter .

you know how customers can somehow get the wrong end of the stick .
 
well certainely a headscratcher alright, seems very strange, maybe the fact both supplys connect to the rod and the fact a surge to earth trips the one may mean the other is over sensitive, must admit it is a funny situation which I am struggling with at the moment.


It is a pain

im thinking of isolating the two earthing systems from each other, having a rod for each and insulating the SWA sheath at the house end from the barn see what happens

just wanted a few ideas for when i get back there

Ramp test the house RCD
 
La de da da da ....any chance of responding to post 2 yet its getting further away as we speak... might be using the 18th edition by the time you respond to it :juggle2:

Please refer to post 21 for guidance.

post 18 :)
 
  • Like
Reactions: 1 person
It is a pain

im thinking of isolating the two earthing systems from each other, having a rod for each and insulating the SWA sheath at the house end from the barn see what happens

just wanted a few ideas for when i get back there

Ramp test the house RCD

Oppps my bad never saw post 18... lol

Ok find the location of the TX relative to the house and barn i suspect if all other scenario's are exhausted i may have an idea.

PS if it is what I suspect you get an arkward situe to address and sometimes its not easy to sort without contravening the Regs.
 
Last edited by a moderator:
I don't think he has enough info yet , he needs access to that house and some test results as well,,,,
 
I don't think he has enough info yet , he needs access to that house and some test results as well,,,,

I have cleared a N-E fault in the barn, all other circuits on that side are ok

will get more info on next visit
 
So where is the single point means of isolation to this farm installation??

Are you absolutely SURE that an earth fault in the barn is tripping the house's downstream 30mA RCD and not the other way round?

Isolating TT earthing systems, what do you think you'll achieve by doing that?? I'd be looking at more towards as to what and how these rod(s) are connected into the system. In fact each building should be roded and then physically connected together. Done properly you could well end up with a neigh on TN Ra value.
 
Engineer 54 wrote;

So where is the single point means of isolation to this farm installation??


there is none!

Are you absolutely SURE that an earth fault in the barn is tripping the house's downstream 30mA RCD and not the other way round?

When the flood lights to the exterior of the barn was switched on they tripped the main RCD in the barn and the isolated 30mA rcd in the house, i have removed this N-E fault but they want to sort this problem as it has happened in the past and a few electricians before me have failed to diagnose the problem, they are also two independant supplies so either way it shouldnt happen

Isolating TT earthing systems, what do you think you'll achieve by doing that??

Although i have not yet been to the house to investigate further, there was a post that was referring to fault current using the house main bonding path rather than the earth rod at the barn as there is no main bonding at the barn end as its all plastic piping , and i know that there is PME connections to local houses so that is probably the case, i was doubtful of whether this is likely to affect the house RCD, but then im a bit short on solutions



I'd be looking at more towards as to what and how these rod(s) are connected into the system. In fact each building should be roded and then physically connected together. Done properly you could well end up with a neigh on TN Ra value.

on this install i would think it fortunate if there is more than one rod lol
 
Engineer 54 wrote;

So where is the single point means of isolation to this farm installation??


there is none! Then one needs to be provided then doesn't it!!

Are you absolutely SURE that an earth fault in the barn is tripping the house's downstream 30mA RCD and not the other way round?

When the flood lights to the exterior of the barn was switched on they tripped the main RCD in the barn and the isolated 30mA rcd in the house, i have removed this N-E fault but they want to sort this problem as it has happened in the past and a few electricians before me have failed to diagnose the problem, they are also two independant supplies so either way it shouldnt happen

Take some photo's of this incoming arrangement and lets have a look...
Should be independent, but depends on how they have been connected, or even possibly interconnected . Farm installations are notorious for out of sight cheap that'll do DIY add-ons and obscure ancient lash-ups. So you might want to have a good walk round to see what you can find... lol!!

Isolating TT earthing systems, what do you think you'll achieve by doing that??

Isolating TT earthing systems from each other isn't going to serve any purpose whatsoever.

Although i have not yet been to the house to investigate further, there was a post that was referring to fault current using the house main bonding path rather than the earth rod at the barn as there is no main bonding at the barn end as its all plastic piping , and i know that there is PME connections to local houses so that is probably the case, i was doubtful of whether this is likely to affect the house RCD, but then im a bit short on solutions

How far away are these other houses in relation to the farm? Unless they are on the same distribution line as the farm, it's doubtful.

I'd be looking at more towards as to what and how these rod(s) are connected into the system. In fact each building should be roded and then physically connected together. Done properly you could well end up with a neigh on TN Ra value.

on this install i would think it fortunate if there is more than one rod lol

Is the farmhouse connected for PME?? On a farm installation, i would personally connect a local earth rod to any and all buildings MET/EMT. Any stray currents will then have a local N-E rod path to run too. But to be effective they need to have a single to very low double figure Ra value...

As i say a few photo's wouldn't go amiss here to show exactly what you have at this farm, at the intake position and farmhouse.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Rcd head scratcher
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
Welchyboy1,
Last reply from
Engineer54,
Replies
35
Views
4,410

Advert