And in any case, 705.411.1 requires RCDs for all circuits "whatever the type of earthing system".
I don’t believe 705 would apply to a distribution cabinet that has no extraneous, no outlets and is inaccessible to animals
 
  • Like
Reactions: DPG
I don’t believe 705 would apply to a distribution cabinet that has no extraneous, no outlets and is inaccessible to animals
I'll take some photo's tomorrow or maybe tonight as I've been dragged there for other reasons.

If we decide the cabinet is 'inaccessible' to animals, and the cables underground are, well, underground, it remains the case that there are distribution circuits supplying points in the field that are not RCD protected.
 
Ok photos.
The distro box D
IMG_6131.jpeg

The more concerning hook up point (the mobile units go before the sheep arrive)

IMG_6132.jpeg
 
Last edited:
1. The requirements for protection against electric shock apply to agricultural or horticultural premises, indoor or outdoor, irrespective of the presence or otherwise of livestock.

2. A distribution cabinet/enclosure is itself included in the definition of electrical equipment, and if it is accessible to livestock, further measures need to be introduced to prevent the livestock interfering with the equipment. (Build a fence around it for example).
 
1. The requirements for protection against electric shock apply to agricultural or horticultural premises, indoor or outdoor, irrespective of the presence or otherwise of livestock.
In locations intended for livestock,

If there is no intention of having livestock, then I'm pretty sure the risk is quite low.
 
  • Like
Reactions: loz2754
Let's not get into a debate about whether 705 applies, for me that is without question as for at least 4 months of a year there are sheep in that there field!

Here is where I am at:

That locked cabinet is the outer cabinet. Inside is a further metal distribution panel with a locked door. It could easily have a fence around it. A fence around it could take it completely out of the special location.

If a lockable front and back panel was made for the hookup points, we then have a distribution box outside the special location, a reasonably sheep-proof box, and every outlet 30ma RCD protected.

Given the history of the reg and taking into consideration the use of the field and the livestock concerned, I'm not considering that it's a C2 that the inaccessible underground cable between the two doesn't have RCD protection. I've asked how deep it was laid and been told 1.2m.
I'll sleep on it but at the moment it's going to be a C3.

If anyone thinks I'm underplaying any risks then let's talk about it; I do very much value the collective wisdom of you lot!
 
If it were me would fit a 300ma RCD at source. Then at the end of the day you have met the requirements of 705.
 
  • Agree
Reactions: loz2754
If it were me would fit a 300ma RCD at source. Then at the end of the day you have met the requirements of 705.
So far every C3 I've issued has been actioned, so it could well still happen.
I'm intending to C2 the livestock access to distribution panel /cables and access to hookups as I consider them more potentially dangerous.
But before deciding on the remedy I need to declare how dangerous a cable 1.2m underneath some sheep without RCD protection is. I'm open to my opinion being swayed by reasoning.
To provoke thinking - if it turned out (as I have no idea) that the supply to the house ran under the same field, would that be potentially dangerous?
 
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the hook up points.
In another life, I have shorn sheep, played midwife to sheep, de-tailed (and other things) sheep, performed chiropodist services on sheep, fed sheep and housed sheep. Hundreds of them. I know how sheep behave, and the only thing they'd do to those cables on the ground is to trample them.
 

Similar threads

D
Replies
5
Views
51
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

timhoward

Broke Internet
Esteemed
Arms
Supporter
~
Joined
Location
Oswestry

Thread Information

Title
Distribution circuits in Section 705 location, RCD needed?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
timhoward,
Last reply from
brianmoooore,
Replies
29
Views
2,681

Advert