The time delay RCD protect the T&E submain when running surface in the garage, underground , then up a dot and dab wall to the consumer unit.

I no it doesn't need RCD protection as its a distribution circuit but surely prevention is better than cure?

I just thought if some one ever damaged it or drills it then the RCD could trip out in 0.04 second? Potentially saving a life?

Or am I getting it wrong as I've never used one before???
 
Regardless of it been a sub-mains supply it would still be subject to the same regulations that all other circuits are regarding 30mA protection unless its was say an SWA .... so i query the fact to it having time delay surely fitting a standard front end 30mA rcd is the way to go and all the board is then protected.... if you didn't want the tripping to drop out the supply to numerous circuits you should have wired it in swa then rcbo'd the circuits.

If you dont have freezers etc in the garage this isn't really an issue and front end protection is fine.

How is the cable protected underground is it fully enclosed throughout in conduit or you just run it through plastic ducting? Also what depth?
 
it's a common misconception that RCDs and Main switches ( e.g. BS 60947-3 ) will trip if the rated current is exceeded. keeep telling guys that the A rating of a switch/RCD is just the load it's designed to carry.
yep....and it would be funny if it wasn`t just so poor....
 
I wonder how many installations out there have circuits protected by an RCD only, ie. where the spark is thinking that the device is giving overload protection as well as the RCD function. There could be a lot of dangerous situations arising from this. Daz
 
to the O/P:
the lads need to know the earthing arrangements for a start...

what type of cable you intent to use for this sub...

whether or not theres any extranious bottom end...

what the max demand is going to be...
 
As dark says, you can't just discard RCD protection because it's a distribution circuit! If it's T&E you will need 30mA, not 100mA TD.
 
Hello David.

The RCD is there for the protection of personnel who may inadvertently come into contact with live a.c. mains. This will not happen on a sub-distribution cable, so no RCD is required for this. The cable itself requires protection from short circuit conditions, and this is what an MCB does. A correctly-rated MCB will be required at the supply end. If personnel protection is deemed necessary for the final sub circuits, this should be provided at the remote end of the supply cable. Nuisance trips become an issue if this is installed at the supply end. If anyone sticks a drill or similar into the cable, the MCB will oprerate and disconnect it.

Regards,

Colin Jenkins.
 
Hello David.

The RCD is there for the protection of personnel who may inadvertently come into contact with live a.c. mains. This will not happen on a sub-distribution cable, so no RCD is required for this. The cable itself requires protection from short circuit conditions, and this is what an MCB does. A correctly-rated MCB will be required at the supply end. If personnel protection is deemed necessary for the final sub circuits, this should be provided at the remote end of the supply cable. Nuisance trips become an issue if this is installed at the supply end. If anyone sticks a drill or similar into the cable, the MCB will oprerate and disconnect it.

Regards,

Colin Jenkins.

still not right!!
pretty sure if no mechanic protection and not surface mounted etc, basically it will need a 30mA RCD and correct rating MCB (or just correct rcbo if no double pole isolation is needed).even if its a sub main feed it can still be damaged.

what type earthing? can it be used?
 
The RCD is there for the protection of personnel who may inadvertently come into contact with live a.c. mains. This will not happen on a sub-distribution cable, so no RCD is required for this.
That's not correct.
The cables of a sub-main are subject to the same requirements as any other circuit.
That is, if new and concealed less than 50mm. from a surface and not mechanically protected then an RCD is required.

Nuisance trips become an issue if this is installed at the supply end.
Nevertheless an RCD is required if installed as above.

If anyone sticks a drill or similar into the cable, the MCB will oprerate and disconnect it.
Not if you only strike one of the conductors.
That is why an RCD is required.
 
A spark carrying out work for people would know this though?? Daz

When you've been told something wrong by a number of people you start to doubt your own knowledge. I was taught in college by more than one tutor that an RCD would trip upon the rated load being exceeded. I was also told this by one of my supervisors at the time. I was ridiculed for questioning my tutors knowledge so I accepted it. Years later on here I was ridiculed for not knowing that this indeed wasn't the case.

Dammed if you do and dammed if you don't!
 
When you've been told something wrong by a number of people you start to doubt your own knowledge. I was taught in college by more than one tutor that an RCD would trip upon the rated load being exceeded. I was also told this by one of my supervisors at the time. I was ridiculed for questioning my tutors knowledge so I accepted it. Years later on here I was ridiculed for not knowing that this indeed wasn't the case.

Dammed if you do and dammed if you don't!
well surely that makes these `tutors` not fit for purpose then doesn`t it Damian...
 
I'd say 90% of tutors these days are not fit for purpose! Most of them have never spent a day in their life on site. They qualify and then go straight into teaching. It is very easy for a younger guy who wants a way into the industry to put muppets like these on a pedestal. Its only when they have a bit more experience and have done their homework themselves that they realise what a sham they have bought into!
 
I'd say 90% of tutors these days are not fit for purpose! Most of them have never spent a day in their life on site. They qualify and then go straight into teaching. It is very easy for a younger guy who wants a way into the industry to put muppets like these on a pedestal. Its only when they have a bit more experience and have done their homework themselves that they realise what a sham they have bought into!
the lecturers at the college i was at were all ex pit guys....all of em had come through the NCB....
although one of em didn`t believe in applying diversity to anything...??????...lol..
 
Hello David.

The RCD is there for the protection of personnel who may inadvertently come into contact with live a.c. mains. This will not happen on a sub-distribution cable, so no RCD is required for this. The cable itself requires protection from short circuit conditions, and this is what an MCB does. A correctly-rated MCB will be required at the supply end. If personnel protection is deemed necessary for the final sub circuits, this should be provided at the remote end of the supply cable. Nuisance trips become an issue if this is installed at the supply end. If anyone sticks a drill or similar into the cable, the MCB will oprerate and disconnect it.

Regards,

Colin Jenkins.

You contradict everything i put here so i call on you to express what regulations allow a submain supply to not require rcd protection as a rule then i show you several regulations that say you are wrong regarding what limited info we have given..... please don't give advice if you don't know what you are talking about and if you think you are correct you need to either shoot your tutor or do a full 3-4yr training course.

PS what would happen if someone drill the dot and dab wall and caught the cable with the live only touching the drill.... the mcb wouldn't trip and the drill may become live....... your advice could be dangerous!

Reading your profile im shocked to find your a consultant yet you just fluffed on what are basic regulations that have been in practice for yrs.... this is not an industrial set-up where the use of swa or all surface mount systems may have been installed this is a supply to a submains in a domestic situe and like every T&E cable it is subject to the same regulations as all the final circuit cables....

Also as highlighted by Glensparks its crucial we know the nature of the supply as well as the construct of the garage to ensure the earthing arrangement complies as it may be a case of he's exported the the earth and left a dangerous senerio.

Shocked i am!! (pun not intended)

Dont get me wrong your knowledge and experience in Electrical Engineering may be valuable but you seem to still hovering on 15th to early 16th edition regarding the IEE regulations but if you think you are correct i dread to think what as a consultant you have got wrong!
 
Last edited by a moderator: