Ok so why am I getting these readings
again...
you says your getting 40ms at X1 and 19ms at X5...hows that a fail...
ramp it again....do it at several points...direct on the device...and at a point close to the device...
disconnect all circuits fed by the device before carrying out the test...
 
and to test the device at a point near to it...disconnect all other circuits fed from it apart of course from the one you are using to carry out the test...but disconnect all loads first..
 
well if its taking 51mA to operate...then its a fail...isn`t it...
a healthy 30mA RCD to BSEN 61008 should let go at about 25-27ish mA
 
You using second hand RCD's?

Never used mcg but on a quick google they look identical to CPN and they are the worst RCD's ive ever seen. I'd even take protek over them and thats saying something.

Buy Hager, you only buy once not twice, thrice...
 
Try one of the RCD's thats failed in the caravan next door - wont take 10mins to put it in, and then put the other good one back.
 