Discuss rcd on a tt system in the UK Electrical Forum area at ElectriciansForums.net
Baker1988
hi ya i have a home work question which is:
What additional protection is required on a TT system, justify your answer, Stating what regulation from bs7671 requires additional protection.
I am sure that answer is a rcd but i just cant fine the reg that states that you need a rcd the closest i can find is reg 411.5.2 but it does not actually say you need on.
any help please
What is higher on a TT sysyem as opposed to a PME system
Hi yes i know the ze and zs is alot higher on a tt system so the overcurrent device might not trip in the required time so you need to fit a rcd as you can have a ze of 1667 ohms and the rcd will still work but i can not find a reg that states this
Reply to rcd on a tt system in the UK Electrical Forum area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...