Discuss RCD on cooker circuit ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
19
Hi all,

Just wanted to hear your views on this one, as im in the process of re-wiring my kitchen.
I have completed my City and Guilds in electrical installation parts 1+2, and my tutor who had 30 years experience in the trade, said you should not put the cooker circuit on an Rcd because it causes nuisance tripping due to earth leakage.
However other bits of info i have read over the months have said otherwise, and that you should always have it on an Rcd.
I will be interested to hear your opinions on this one.

Thx.
 
If the cooker point has a socket outlet i always but it on a RCD, However if you are pulling in a new circuit for the cooker it should be done to 17th which really means it should be RCD protected anyway
 
your tutor is right it can cause nuisance tripping but as mentioned, under the 17Th basically everything has to be on an RCD unless the cables are enclosed in earthed conduit / capping
 
What your tutor may of meant was not to put the cooker on a bank of mcb's protected by a RCD but put it on a non RCD protected way with a RCBO.

Reading that, i have confused myself:eek:
 
your tutor is right it can cause nuisance tripping but as mentioned, under the 17Th basically everything has to be on an RCD unless the cables are enclosed in earthed conduit / capping

Not necessarily, provision exists for dispensing with RCDs in specific circumstances. eg 314.1 (iv) designated/marked circuits etc but if the cooker point has a socket then no matter whether it's suitably marked there is nothing stopping Joe Public running an extension lead through the kitchen window to the cooker socket therefore the requirement for additional protection (reg 415.1) has to take priority.
If diagnosing a cooker that's tripping an RCD it's an idea to get an idea of the appliance's PEAK leakage current in its cold condition as it will be at switch on from cold when the cct. resistances are at their lowest so will allow the maximum leakage currents to flow. As it heats up they will lessen. If there's no fault with the wiring and the tripping is confirmed as excess leakage from the appliance you swap the skt. equipped cooker control for a simple DP switch and transfer to non-RCD protected side.
 

Reply to RCD on cooker circuit ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
633
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
307
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
773
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
213
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock