Discuss RCD protection for cables above a plasterboard ceiling in the UK Electrical Forum area at ElectriciansForums.net
TJC1
Are there an reg for cables being above a plasterboard ceiling?
Pricing a job to move a kitchen to the other end of the house. I thought about running a 16mm T&E to a submain board instead of running 4/5 circuits back.
The old kitchen ceiling ceiling is coming down and the rest would be ran in trunking to the new kitchen. So a mixture of above a ceiling/clipped direct/in trunking
I cant see a reg other than buried in a wall that would apply..... it wont pass through any bathrooms either
T
In near every case a cable run through the fabric of the house will be buried less than 50mm at some point in the run. (Unless fully surface wiring job)
But if 100% isn’t buried less than 50mm I don’t see the need for rcd protection.
But probably would anyway imo
Its true. But i dont want all 5/6 circuits at the new kitchen to be on one RCD and i cant wire it in swa :(
Sounds like your 16mm is going to be a distribution circuit and not buried in a wall. You can always protect your final circuits with an RCD or RCBOs so if it's just above a ceiling you should get away with it
Reply to RCD protection for cables above a plasterboard ceiling in the UK Electrical Forum area at ElectriciansForums.net
Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
With current regs is 50mm enough, I know in floors they should be 50mm clear of the plasterboard, but this is a flat roof with vapour barrier and...