Discuss rcd protection for power circuits in the UK Electrical Forum area at ElectriciansForums.net
yes, i agree with that. the confusion arises over whether it.s necessary to fit RCD protection at the source of the circuit that you have worked on or just to protect the new cable/accessories. one argument is that because you have worked on a particular circuit, then that circuit in it's entirity should conform to current regs..
Yes but the alteration must comply with relevant regulations do they not?
And yes "special location" sorry .... should have been more like "a place of danger where a RCD should not be used".. ^^
Compliance with the Regulations can be achieved for instance by spuring off the existing circuit using an RCD FCU.
Another option might be to add an RCD socket back to back with an existing socket-outlet.
Always assuming that RCD protection is required for the socket-outlets.
There's no requirement to protect the whole circuit, unless of course you are installing a socket-outlet in a bathroom, or the installation is Agricultural/horticultural.
As for the lawn mower comment, I doubt very much that my Suffolk Punch will be any safer because I've got an RCD.
However it is a requirement to provide additional protection by means of an RCD for mobile equipment used outdoors.
Still doesn't require the whole circuit to be RCD protected.
No one in their right mind is going to install seperate circuits to accomodate the compliance with regulations.
anyone got a 50way CU that I can pick and choose which circuits I place on RCD and which I do not?
Its my real name IDC , your problem is if you are reported you will probably never get work.....
I think you'll find, that the majority of sparks (as in all but you), will install separate circuits.
They may not install them to accomodate compliance with the Regulations, they may install them for convenience, or simply because it's good practice.
As for needing a 50 way CU in order to be able to pick and choose, it's just not necessary, a 4 way will suffice.
And you ar ehow old? for interest only?
Could be earthed metallic sheath, earthed conduit or trunking, mechanical protection sufficient to prevent penetration by nails or screws or can be run on the surface of the wall.
Yes of course, but then again when the customer says they don't want surface trunking, then I don't think that the use off mechanical protection is the next method on the list of the majority of electricians.
In reply to the OP, then the addition of the RCD is 99% of the time going to be the chosen method i'd of thought.
Reply to rcd protection for power circuits in the UK Electrical Forum area at ElectriciansForums.net
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Hi, just hoping for a bit of advice. When I travel abroad (Europe, predominantly Spain/Cyprus) I usually take a single travel adaptor and a UK 4...
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...