Power Ranger, it has already been confirmed that there are no parallel paths at the start of this saga as the rcd tripped no more when the naughty boy took the cpcs out of the met.
The lesson in this thread is that you can take a horse (aka Electrical Trainee) to water but you cannot make it drink.
Oops, no, I dont have a horse parked outside customers houses, said it before Biff.

Boydy
 
Ah lesson learned today: read all posts in a thread before posting myself.

Just an IR test between line and earth was the most logical thing to do. .. I dont understand why this was not carried out.

First thing to do should have been an IR test...
 
Power Ranger, it has already been confirmed that there are no parallel paths at the start of this saga as the rcd tripped no more when the naughty boy took the cpcs out of the met.
The lesson in this thread is that you can take a horse (aka Electrical Trainee) to water but you cannot make it drink.
Oops, no, I dont have a horse parked outside customers houses, said it before Biff.

Boydy

Boydy, Yes of course, your right on that count in that its obviuosly a L-CPC fault on this circuit. So apologies if I caused a bit of confusion on the thread as Sirocco would still have found the fault doing IR tests with the CPCs disconnected at the MET.

However, if he had removed a few sockets including the one with the fault on it before doing any IR tests then he would have probably cleared the fault on this occassion and so would have not found anything wrong. Therefore, I probably now guess that as the RCD is holding on that the fault would now be only found on close visible inspection of the Line conductor insulation at each outlet.

But what I was originally getting at, is that quite a few electricians do their IR tests with the CPC's isolated from the MET and I just got the impression that Sirocco always did this as part of his normal testing procedure.
 
rcd help!

When i rcd test with my fluke meter it works on some circuits and on the rest it reads 310.0 Ms an wont trip!! Wots up?? Please help!
 
Re: rcd help!

When i rcd test with my fluke meter it works on some circuits and on the rest it reads 310.0 Ms an wont trip!! Wots up?? Please help!

How are you testing? more info needed.
Not familiar with the fluke but it's probably going over-range at 310ms. Make sure all loads are disconnected before testing,as these can cause longer trip times,particularly loads with a capacitor.
 
Hi
Have this with my fluke occasionally, only when I test at rcbo/ rcd but if test at end of circuit it works ok. Hope this is of use.
Regards
Gary
 
Hi
Have this with my fluke occasionally, only when I test at rcbo/ rcd but if test at end of circuit it works ok. Hope this is of use.
Regards
Gary


Which goes against virtually all of the RCD/RCBO manufacturers testing procedure recommendations!!....
 