Hello, been at a job today where I am adding in new lights,fan etc into new bathroom.

old rewirable db, with a 4way rcd board added in for downstairs bathroom .

So, to cover my work I ir tested upstairs lights circuit with the intention of moving this circuit to the 4way rcd board , all ir testing results tested ok, but when I connected into rcd board and attempt to put any load onto the circuit (switch a light on) then the rcd trips.

Relatively inexperienced when it comes to fault finding and I understand the borrowed neutral problem causing issues when two rcd's as per new17th board, but couldn't understand why the rcd tripped in this instance?

The 4way rcd board is supplied by 16mm tails which have been split so supplying both the old rewirable board and the new 4 way rcd board.

anyone help ?

thanks
 
That's the thing tho I haven't connected anything new to circuit yet, just stripped out some old wiring not required any longer.

Can't think that anything I did in that respect has caused a problem.

Just was left scratching my head this afternoon as to if I'd missed anything simple as to me both the rcd board and the old rewritable still had a common neutral so couldn't understand why the rcd would trip
 
Yes I'm thinking probably borrowed neutral but as both the rcd board and the old Wylex rewirable board supplied from same neutral block I couldn't see why ?
 
Test between the neutral for the lights that keep tripping and the other neutrals on the consumer unit. Will determine if it is borrowed.
 
No worries.
Test between neutral bars and look for interconnection. If not, then there may well be a n-e short.
Drawing out the situation may help you understand why it trips when the neutrals are connected wrong. :)
 
Turn the whole lot off at the main switch - safe isolation procedure, then separate the lighting neutrals out of the board and test to see if there is any connection between them at low ohms and then at IR. if there is that is your problem, if not put the then you will need to test that the live going out on the live to upstair only comes back to the neutral upstairs - to do this with the neutrals still disconected (but put in chock block to be safe) power up the upstair live and check for voltage on the upstairs neutral and the downstairs neutral (when a light is switched on upstairs) if it comes on both they are interconeected, if it comes on the down neutral you have a borrowed neutral. Google it and you will find loads of diagrams and remedies. Good luck
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Rcd trip
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
currie123,
Last reply from
martinxxxxxx,
Replies
10
Views
1,309

Advert

Back
Top