Thanks to allSome RCD will trip if the polarity is wrong (i.e. L and N swapped) or if there is no CPC (earth) connection. Both faults are very serious so it needs to be identified and fixed urgently!
You might be best to get a professional electrician in.
But if you feel you can (or want to) identify if it is the socket at fault or there is something odd with the RCD adaptor then you could try one of these:
![]()
TIS Socket Tester With Loop & RCD Check | Toolstation
A pocket sized checker for indicating loop impedance, socket polarity and RCD 30mA are all ok. Indication is by LED's and buzzer. An ideal unit for initial "checking out" of a 13A socket and will advise if the circuit is ok, needs attention, or needs urgent attention. An ideal product for...www.toolstation.com
Please be aware that even these better quality socket testers are still limited in what they can tell you about the status of the supply socket. If they tell you it is faulty then you can be very sure it is, however, if they give the all-clear you might still have some subtle faults present. The cheap ~£10 socket testers are not that good though as they will pass a socket with wet string for the CPC!