I would also double check that the black insulated core was connected to neutral at both ends and the bare conductor with bodged black sleeving is connected to earth - and also replace with correct green/yellow sleeving.
 
  • Like
Reactions: timhoward and DPG
I would also double check that the black insulated core was connected to neutral at both ends and the bare conductor with bodged black sleeving is connected to earth - and also replace with correct green/yellow sleeving.
Thanks - yes I want to replace sleeving once I find the cross over.
I’ve decided to draw it all out on paper as a first step!
 
  • Like
Reactions: Dave OCD
Probably start in the middle somewhere and find it with a voltstick then confirm

If that's what you're saying?

You've got reverse polarity at an outlet and you don't know where it originates
Yes I’ve got socket tester reporting L and N reversed and a rcd tripping implying L to E somewhere.The socket is at the last stage of socket - fuse box. - fused spur - main CU.
 
Yes I’ve got socket tester reporting L and N reversed and a rcd tripping implying L to E somewhere.The socket is at the last stage of socket - fuse box. - fused spur - main CU.

You'll probably need to IR test so, as well as find the reverse polarity
 
wander lead would be useful here. can make up a temp. one with a length of scrap single.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Stevenage
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Spouse of an advanced city and guilds electronics Lab technician (retired) and DIYer

Thread Information

Title
Rcd tripping cause?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Ziggie,
Last reply from
telectrix,
Replies
24
Views
4,834

Advert