Try taking the all the neutrals out of the lighting circuits on the non rcd side and switch on the lighting breakers temporarily.Try the pelmet lights.If they are still on then they have borrowed the neutral from the RCD side.Also after putting everything back together,see which breaker isolates the pelmet lights just to make sure it's not on the rcd side.
i'd be very careful here. with the neutrals dissed from supply N,they will become energised to 240V with loose ends floating about.a dangerous practice, IMO.
 
A few questions and thoughts:

1. What earthing system?
2. Are the pelmet fittings earthed or double insulated?
3. What final circuits are protected by (a) RCD and (b) no RCD?
4. Any water leaks recently?
5. IR test results?
6. PAT test results of appliances with a heater element?
7. Has the fault started since we have had rain?
8. Is the switch single of double pole?
9. Check polarity of pelmet circuit and kitchen light circuit.
10. EP bonding correct?
11. Isolate each pelmet until non are connected. Check IR of pelmet fittings.
12. Swap the switch.

Thanks for reply
1 TNC-S
2 earthed class 1
3 RCD, SKTs,Boiler,Cooker,Water heater
None RCD, Lights
4 No leaks or any works been done
5 >200
6 Haven t done that
7 didn't ask that question
8 single
9 polarity correct
10 yes
11 done that its correct
12 your the second person to say that so will do although im not convinced haha
 
A few questions and thoughts:

1. What earthing system?
2. Are the pelmet fittings earthed or double insulated?
3. What final circuits are protected by (a) RCD and (b) no RCD?
4. Any water leaks recently?
5. IR test results?
6. PAT test results of appliances with a heater element?
7. Has the fault started since we have had rain?
8. Is the switch single of double pole?
9. Check polarity of pelmet circuit and kitchen light circuit.
10. EP bonding correct?
11. Isolate each pelmet until non are connected. Check IR of pelmet fittings.
12. Swap the switch.

Thanks for reply
1 TNC-S
2 earthed class 1
3 RCD, SKTs,Boiler,Cooker,Water heater
None RCD, Lights
4 No leaks or any works been done
5 >200
6 Haven t done that
7 didn't ask that question
8 single
9 polarity correct
10 yes
11 done that its correct
12 your the second person to say that so will do although im not convinced haha
Try taking the all the neutrals out of the lighting circuits on the non rcd side and switch on the lighting breakers temporarily.Try the pelmet lights.If they are still on then they have borrowed the neutral from the RCD side.Also after putting everything back together,see which breaker isolates the pelmet lights just to make sure it's not on the rcd side.
 
next thing i'd do is replace the switch. possible transient caused when it switches off. simpleand cheap. if it fixes, fine, if not then FI.
 
If all else fails employ one of these:

bloodhound-following-a-scent-HNGCD7.jpg
 
I have just returned from walking Mabel - our Jack Russell and realised I forgot to suggest you inspect, test solidity of and where required tighten up connections, especially Ns and cpcs.
 