i'd be very careful here. with the neutrals dissed from supply N,they will become energised to 240V with loose ends floating about.a dangerous practice, IMO.Try taking the all the neutrals out of the lighting circuits on the non rcd side and switch on the lighting breakers temporarily.Try the pelmet lights.If they are still on then they have borrowed the neutral from the RCD side.Also after putting everything back together,see which breaker isolates the pelmet lights just to make sure it's not on the rcd side.