M

MICKYSPARKY

just changed CU at domestic proprty, re-energised circuits found all cicuits except ground floor lights keeps tripping. after lifting floor boards to inspect wiring noticed first light on cicuit is fluorescent live, neutral earth conections, found the earth was picked up from ring main JB, all lights after were single core live neutral no earth. found that the neutral on this circuit is permanently live, even when i disconnect from the CU, any info please
 
ks like the favorte old trick of borrowed neutral from another circuit for the lighting. Have they taken the nutral from the downstairs lighting circuit?
Had this before where the stair lights 1x bottom light + 1x top light switched togethersame line cct, but neutrals were h from differenet circuits - makes no difference as far as the old rewireable fuses are concerned - but will never get an RCD to stand up.
 
if you disconnect the N from the CU, it WILL be live, due to the fact that all the circuit will be sitting at 240V. looks like you need to do some serious investigation here. linked circuits, bodged up JBs, shared |Neutrals, etc.
 

Reply to RCD tripping, lighting circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
675
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock