Ill reiterate what i said before fully disconnect and get a knowledged competent person in ...Electrician means nothing nowadays with all the short courses and fast track qualifications so ensure who-ever you get is fully experienced with gen' set-ups...You could always fly E5 over and ensure a quality experienced knowledgeable sparks or taxi Marvo over as very good advice has been given ... anyone else you will need to vet them and ensure they aint just your routine sparkies!
As i said before you clearly have a bit of grasp of electrics but i fear not enough for this situation and as you have realised you maybe at risk here ...... a little knowledge is very dangerous sometimes!
gen has N tied to E and its own Earth so I have added a further earth- I could switch the earth so the gen and house earth are independent but I can see no reason why this should be necessary.
So what do you call this, if not mixing the earthing systems then??
With PME you need automatic earth transfer to safely use a generator. This gets messy and very complicated, if you try to do this on your own.
You can’t use the PME earth for your generator.
You say you now know what DNO means, I think they would love to see this set up. It is downright bloody dangerous and they will remove you’re supply and PME earth immediately.
So you have two options, scrap the generator or employ an engineer that knows what they are doing.
No I’m not offering my services:
YOU CAN’T AFFORD ME!
Personally:
I think this is a very well put together Troll thread. A knowable Troll I’ll grant. There are far too many inconsistencies.
Biff!
It’s time to doff you’re cap!
I had guessed the earth may not be set up correctly.
The gen spike tied to the N at the gen is on good copper and is as close to the gen as possible - about 1m away. It consists of a spike about 1.5m long.
What I don't quite understand is what additional risks or benefits are involved in switching the earth system.
Currently because the Utility N is switched then so too is the utility E,
So on gen supply the earth is entirely to the gen spike. There is no utility earth.
On utility feed there is both the gen spike and utility N tied.
Now I could switch out the generator earth but I can't see that being the issue.
Incidentally the earthing system to the gen is on really heavy gauge copper - looks like three core car battery cable - the gen earth was tested by my electrician and they seemed to think it well within spec
I don't have test kit myself beyond a little meter but I have checked if there is any pd between the utility E and the gen E (when the two aren't connected obviously) and there is no pd.
What is interesting is that there is a regulation or best practice in having utility spike and gen spike a set distance apart.
My guess is that this is to prevent a potential backfeed to the grid from one earth to the other - so if a gen fault creates a current to earth it doesn't then find its way back into a nearby earth spike along the utility to a lower resistance E.
The is no chance of that happening since the only earth spike in on the gen.
So what would I gain by switching earth systems? I would gain a momentary period where the entire house has no earth at all.
Am I at risk from a utility fault? Potentially I could now be earthing the grid if their E was not as good as mine?
The AMF I have is 3 phase capable but I'm on a single phase supply so I can easily switch the earth using spares on the contactors but really not sure what I'd be gaining.
Either that or add a furthe spike and earth the PME again?
Tony - nothing troll going on. Honestly I'll take a picture with today's newspaper of the whole job if it helps!
... OK local electrician contacted. He asked all the right questions but doesn't seem like there is an immediate answer. Should know more later today when they visit.
Some of the most dangerous lines ive seen on this forum in a long time regarding the theme here.....although we still lack info to give confident answers their is a risk that this set-up is a death-trap for your family ..... il reiterate that point because of the casual nature of your posts and openess to expressing you don't understand a lot of what you've done .....Advanced DIY it maybe, your enthusiasm to understand what you have done is commendable but you really need to appreciate you are clearly out of your depth with possible deadly consequences ..... we await your pics and will be interested to see what the electrician says....
Not sure how to comment the images but looks fairly straight forward to me once you chase the wires back to something you recognise. Probably not so easy from a picture.
Supplies to contactors go in the base and out of the top. The one on the right is connected to the CU and the one on the left is bridged over so the gen supply does the same when switched.
You can see how simple it would be to switch the gen earth. But there is a less obvious issue. There is a 12v circuit for gen battery and power to the computer. So switching out the gen earth would also switch out the DC neg since this is grounded to the gen chassis. This is normal and best practice I have looked at other setups and they all earth the gen battery to the gen chassis. So I don't think there is a way to switch the earth. Maybe I need another control battery which is not earthed to achieve this but again this isn't seen in other gen setups.
As Darkwood has suggested let's wait until the electrician(s) that are coming today, look over you're system and come up with a solution.
One thing i would suggest to you, is to ask them to re-dress the house and generator supply cables in that ATS. As it stands at the moment it's a bloody abortion of a job.
I don't think a single 1.2m earth rod for a permanent Stand-By Generator is sufficient to be totally honest, especially if it's one of these 3/8'' twigs. If this earth rod has a screwed end it will be a 5/8'' rod that can be extended by use of a coupler... If not then discard the old rod and drive in 2 X 1.2m X 5/8'' rods for the generator earth. Then get the electrician to measure the rods Ra, the lower the value the better!!
Anyway, let's see what this electrician has to say about your problem and the overall installation of this gen-set....
Well, an electrician has taken a look but no further forward. Theories now surround faulty RCDs - so it looks like further expertise is needed to get to the bottom of it.
So independent separate rcd's all suddenly go faulty .... sounds like you got your everyday basic domestic electrician there.... did you question him on his proficiency with back-up supplies and supply arrangements?
I'm afraid you're going to have another look for a qualified proficient electrician that knows a lot more, than just domestic wiring.... You may have to call on the services of a bonafide electrical contracting company, that covers among other things, industrial/commercial installations and maintenance....
Can you post close up's of all the RCD devices you have in place at the moment, preferably with the enclosure covers off?? A photo or two of the gen-set would be nice too showing the connections and earthing and control panel interior...
You've had me thinking . Wot you have with ur common'd you're pme earth with the gen earth witch is also pme'd?? . I understand the earth is pmd! So to speek at both dno side and generator wot you have is maybe as ur contractor lets say gen side cuts out ur rcd may momentarily detecting a foreign current down earth as the contractor has isolated the line and neutral but neutral and earth at equal potential . So I'm thinking you may need to run the earthing conductor via contactor ? I apologise I'm no shakspear absolutely hopless with words ( and spelling a true engineer lol )