It's naughty, whichever way it came about. With any load on the E7 board, in the event of a trip the house blacks out, but every single point is still live, both on the E7 and the 24h and there is more risk of shock with the RCD off than on. It's a good thing it was self-incriminating.
 
Aico 3000 Range
This official sponsor may provide discounts for members
  • Thread Starter Thread Starter
  • #30
It's naughty, whichever way it came about. With any load on the E7 board, in the event of a trip the house blacks out, but every single point is still live, both on the E7 and the 24h and there is more risk of shock with the RCD off than on. It's a good thing it was self-incriminating.
it's a good point.... but, as it stands, with the rcd tripped, the only live would be to the E7 cct, both live & neutral to the 24h cct would be isolated.
Post automatically merged:

That is your problem. The line and E7 neutral are creating an imbalance as one uses the rcd while the other does not. If you have a TT system and that is the only rcd then the E7 circuits a not likely to have fault protection. The E7 needs a separate rcd with its neutral taken from before the current rcd.
Post automatically merged:

This is the set up you require.View attachment 53677
great!.... got the bits, just consuming last supper (well, lunch actually) and i'll be at it !
 

Lucien Nunes

-
Mentor
Arms
Esteemed
as it stands, with the rcd tripped, the only live would be to the E7 cct, both live & neutral to the 24h cct would be isolated
No they wouldn't, if there's load on the E7 DB, that's why it's so dodgy. There's a path from E7 line, through the E7 load to the E7 neutral bar (which is now at 230V w.r.t earth), via the splitter block to the 24h neutral bar also now at 230V, through the 24h load to the 24h line. There's no circuit to supply neutral so none of the loads work and it all looks dead as a dodo, but every conductor in the installation is sitting at 230V via the loads. The resistance of a heater in series makes no practical difference to the severity of an electric shock. And there's no RCD protection.
 

DPG

-
Arms
Esteemed
I would get an electrician in to give the installation a thorough check. For your own peace of mind.
 
  • Thread Starter Thread Starter
  • #35
No they wouldn't, if there's load on the E7 DB, that's why it's so dodgy. There's a path from E7 line, through the E7 load to the E7 neutral bar (which is now at 230V w.r.t earth), via the splitter block to the 24h neutral bar also now at 230V, through the 24h load to the 24h line. There's no circuit to supply neutral so none of the loads work and it all looks dead as a dodo, but every conductor in the installation is sitting at 230V via the loads. The resistance of a heater in series makes no practical difference to the severity of an electric shock. And there's no RCD protection.
yes, unless all the mcb in the E7 CU are off
Post automatically merged:

I would get an electrician in to give the installation a thorough check. For your own peace of mind.
he was coming monday pm anyway... so (by law, i believe) i need to have it checked out for cockups and/or poor workmanship
Post automatically merged:

how better to spend a wet afternoon ....
neutral split via new JB, new rcd fitted (80a) new tails where needed.
ccts are independant of each other now, each with own rcd.
what can possibly go wrong ? :)
thanks for your help guys, hopefully SWMBO will be nice and warm tomorrow, and i'll have lots of brownie points ....
will report back in the morning
 

Attachments

Last edited:
  • Thread Starter Thread Starter
  • #38
ok.... system working fine (well, apart from the fact that i failed to switch on one of the heaters ... doh) .... i checked them at 4 this morning (and switched on the one i left off last night !).
So, big thanks to you guys... saved me a lot of time and money, although i will still get it all checked by Mr Sparks on monday.
on reflection.... i'm a bit ----ed off with whoever fitted the new meter, and left the system in a dangerous state, i'm just lucky that i had no loads on the E7 side and the mcb was off. AND it cost me £100 plus to remedy, on the plus side thankfully no-one got hurt....
thanks again
 

Reply to RCD tripping when E7 switches on in the Electrical Forum area at ElectriciansForums.net

Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top Bottom