K
Keefyjet
Hi,
As I understand, touching or cutting the earth core of a disconnected (via its MCB) circuit can cause an imbalance and an RCD trip – due to other working circuits connected to the same RCD bank.
So why doesn’t touching the earthed part of a working appliance (e.g. the chassis of a tumble dryer) cause the same imbalance and RCD trip?
Maybe I’m missing something blindingly obvious here – in which case please enlighten me.
Regards.
:21:
Are you sure it is earthed?
If your washing machine body is earthed and on a TN-C-S system the "Earth" and Neutral are effectively the same thing as they join together at the supply feed. You make a connection between your 'washers' CPC and the 'washers' neutral then it allows other circuits current an alternative path back (i.e. some current flows up the 'washers' neutral and down the 'washers' earth so passing the RCD and causing the inbalance).
There are a few assumptions there, the biggest being that you dont have a double pole 'washer' MCB and the neutral is isolated!
Not sure what you mean by touching the chassis of a tumble dryer? Touching with what? Your hand....?
Yes, as in providing another earth route, in this case via ones body. Why doesn't it unbalance the system in the same way as touching or cutting through the earth cable?
Disclaimer to this thread
Your understanding is appreciated
This new technology is only just a recent introduction to us in Wales
Touching an earth core shouldn't trip an rcd.
cutting the cables ( shorting the N & E) usually does
It depends what you touch the earth with, i'm confused aswell by the OP lol.
Stick your manhood on the earth, and you wont trip the RCD and if everythings in working order you won't get the thrill you're probably desiring.
Stick a line conductor on the earth, then you'll trip it.
Mr.Keefyjet what do you mean by touching the metallic frame of an appliance? I hope you're not suggesting, why should it not trip when you pick it up lol
I suggest reading up on earthing and bonding.
a pilot project in south wales introduced indoor toilets and bathrooms to a few select houses. when it was found that said toilets and bathrooms were being used to bath and shear the sheep, the project was abandoned in favour of underground housing, but those resourceful taffs kept coming back to the surface bringing up the coal.
Yes, the neutral is common but, as I understand it, the imbalance causing the RCD to trip occurs only if one or more of the other circuits under said RCD bank is/are in use? In other words if all of the circuits under the control of that RCD had no load the RCD wouldn't trip as there'd be no imbalance for it to detect?
I have to be honest and say this is the second thread that has had me confused
The earlier fuss about the bath in the bedroom
Our own baths in Wales would be in whatever room was the warmest
If it wasn't there,it would be on the nail in the yard
on the nail next to the vet's trousers when he was doing the artificial insemination bit to the cow.
Maybe i've misread the OP but i took it that it was 2 seperate unrelated questions...
the whole thread is unrelated now., it's well past beer o'clock and silly threads get sillier.
It's past beer o'clock, but it's not quite reached the missus going to bed "i'll be up in a minute" quick look a babestation because we're mucky men thinking we were still 18 o'clock.
HAHHA
Thats not me btw(honest sir), just my impression of what Geordiesparks like come bed time LOL.
An RCD works on the balance of current flowing through it (only through the line and neutral). If you isolate the circuit via the MCB and then cut the cable, you will join the earth conductor and the neutral conductor, thus allowing some of the neutral current (from the neutral bar in the CU) to travel via the earth conductor in your isolated circuit.
This then causes an imbalance in the RCD and trips it off.
The reason why an RCD won't trip when you touch the casing of a metallic appliance, is due to not causing any imbalance of current through the RCD.
Classic case of overthinking the question.
@OP: Your original assumption (and hence the title) is wrong and misleading. Touching or cutting the CPC ('earth') of a circuit, regardless of whether the circuit is energised or not, does not trip an RCD. Therefore, there is no question to answer about why touching the case of an appliance does not cause this. As others have explained, it is making contact with the neutral that is the issue.
Re post 15, the assumption here is not correct either. If there is a potential between neutral and earth at the origin, e.g. with a TN-S system, even without load on the system the RCD might still trip when N & CPC are shorted by cutting the cable. If the installation has load on other circuits (which need not be on the same RCD or CU) it is more likely that there will be enough p.d. between N & E to pass a current above the trip threshold through the N-CPC short.
RCD tripping when earth core touched
Keefyjet,
Lucien Nunes,