Discuss RCD tripping when switching oven isolator off in the UK Electrical Forum area at ElectriciansForums.net
streamer
Hi all.
I was called to a house recently where the occupier reported that when they turned the oven isolator off the RCD would trip.
So I tried it and that's exactly what happened. There was nothing switched on on the oven at the time. When the oven is on it works fine.
It is an integrated oven on a dedicated 16 amp circuit. Circuit tested fine in all respects and a ramp test on RCD showed it tripping at 24 mA.
They have to turn the isolator off when not using the oven as they have a son with learning difficulties who sometimes turns the controls on the front of th oven.
Any ideas what the cause might be?
Thanks.
Did you try an earth leakage clamp.on the circuit? It is possible that there is a spike when turning it off which is pushing an already close RCD over the edge, it's a long shot but I have seen it happening
as post #4. try replacing the isolator before the head scratching.
Edit as previously mentioned. Have a look at the Beama RCD guide, section 9.3. Could be a possibility
  • RCD Handbook (Dec 2010) (6).pdf
Replace the DP switch with one which makes the neutral before the line and breaks the line before the neutral. I think MK cooker switches operate this way.
Understandable for a 3ph DB main switch for example.
However, this shouldn't in theory effect a single phase load. There isn't a difference in current draw, by switching line or neutral.
Unless the switch is faulty and is sending some current elsewhere.
Beama talk about 'Double pole switching within the fixed wiring is known to produce a strange phenomenon whereby switching OFF a double pole switch supplied through an RCD can cause the RCD to trip.' in their RCD Handbook.
So there must be some substances to it.
The only thing I can think of, is it causing some from of capacitive spike in the cable.
Re #14: The sequence of switching of the line and neutral does affect the changes of potential differences of the line and neutral conductors with respect to earth - and because of this there is the possibility of transient current flows through the line and neutral conductors distributed capacitance to earth which does create a differential current through the RCD. Plot out the changes of potentials/currents for the equivalent circuit and you will see what happens - which is why in earthed neutral systems single phase DP switches are make N first break N last - so N conductors remains at earth potential - ie do not momentarily jump up to Line potential then down to zero to avoid nuisance tripping of RCDs.
Yes, as soon as I stopped an actually thought about it, I realized what could happen.
Had this on a board change I did a while ago.
Customer reported rcd tripping when they turned the cooker off.
I must say this was the first time I have come across this particular problem
Reply to RCD tripping when switching oven isolator off in the UK Electrical Forum area at ElectriciansForums.net
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...