N
Nickj
Hey all,
Downstairs lights are off. When you put the mcb on the rcd instantly trips.
I've done an insulation resistance test and I have >20MOhm on L-N, L-E, N-E.
I've checked the wiring at all the roses and all seems secure and correct.
What could be causing this?
There are 4 ceiling roses, one porch light, one toilet light with fan, one kitchen light (5 GU10's) and one outside light.
All bulbs have been removed and all switches are in off position.
My voltage tester picks up a continuity between line and earth at the ceiling roses, however when tested with multi tester it indicates no continuity between the two.
The house does have a damp problem.
I did remove the line connections on what I think is the first light on the circuit however the RCD still tips.
I'm totally confused by it
Thanks,
Nick
Hello and thank you,
No work has been done to the house. I've been away however according to my aunt who was at the house it happened sometime around the major storm we had. It being a damp house I suspect it's caused by water/moisture however would that not show up on insulation resistance test?
It might, but there isn't any guarantee that testing will find a fault. This is why the term "inspection" comes first in the phrase "inspection & testing". It is done first, but is also more important than testing. Testing merely supplements inspection.
That said if there was a lot of damp you would probably expect to notice that when insulation testing. But there could be other reasons not related to dampness for your problem.
With all the lamps out does the RCD still trip once the MCB is switched on or does it hold ?
I take it that the RCD is tested and is working?
Hello and thank you tony mc,
Yes all lamps are out, all switches are off. Even in that state the rcd trips when the mcb is switched on. RCD is working.
I'm at a total loss at to what to do next
Based on your test results there is a problem from switched line to earth (possibly via neutral).
Since you tested with the switches off and loads removed the switched line core from the switch to the light fitting was not included in the test.
When you are testing at the ceiling rose then this is indicating a fault (with a voltage indicator?).
Leave the switches off and test IR at each light fitting from switched line to earth and one (or more) of them will show a low IR result.
If it is associated with storm conditions then I would start with outside lights and lights in the loft.
It seems strange that you are getting 20Meg on your test but on resetting the Rcd it trips instantly.
How many other MCB's are protected by the RCD and have you tried switching the other MCBs off and removing the neutrals to see if the RCD holds when the light MCB is reset?
The thing is OP....if the IR really is >20 megs, and the RCD is not faulty, and the circuit is correctly connected in the DB....it wont trip. The only reason I can think of where you may be missing a fault is if you are disconnecting the earth at the DB to test,and there is a L or N fault to earth via a damp wall or something which is may not show up to the cpc. If you are disconnecting the cpc at the DB try an IR test L/N to the earth bar in the DB, or leave the cpc connected.
I will try this when I'm next home on Wednesday ad see what results it gives. Thanks for at least giving me another avenue to explore
2 other MCBs protected by same RCD. I did swap the downstairs lights with upstairs (and moved neutrals over). Upstairs lights still worked on the previously downstairs RCD but downstairs lights tripped on the previously upstairs RCD as well.
i've had a similar fault on a socket circuit. RCD trips as soon as you energise the MCB. IR test gave >100Meg. turned out to be a nicked L cable in back of a socket, arcing to the back box. with socket fronts pulled forward there was no tripping. soon as 1 socket in particular was screwed back, RCD tripped.
I ran the IR test with all wires still connected so -
MCB -> Earth bar
MCB - > Neutral bar
Neutral bar -> earth bar
I didn't expect to get > 20 MOhm so I then disconnected the live neutral and earth wires and tested with just the wires.
Still > 20 Mohm -> Scratches head
Nickj,
Perryway-,