some help at job last night the rcd triped out after 3 or 4 minites after power was switched on it when re set it tripped out again . rcd is 63 amp 30ma cragtree any help
johnnb i am not that daft mate done all that i disconnected all cables from the mcbs tested rcd with my meter it tripped off at 1% in 14ms and at 5% 34 but with no load on it it only lasts 3 to 4 mins think for you help new new rcd incomer req
. Also at what rating does the rcd trip at? they generally trip at around 24mA.