Just been called to a tripping problem in a lab,where 3 seperate rcds would trip out for no reason.After some time discovered a heat damaged neutral connection in a seperate db in another part of the building.With this connection repaired ,the tripping problem ceased.Can any one explain this .:dizzy2:
 