We are suppling an outside portacabin with a steel wired armoured 3 core cable live neutral earth from a TN-S system. Does the portocabin reguire an earth electrode and does the origin of the supply have to have an rcd/rcbo fitted with a rcd and also fitted on the consumer unit inside the portocabin.
 
Hey.

We do a lot of portacabins for local schools and the way I do it for TN-S is 25mm3c swa protected by 100mA RCD and 60A switchfuse at the origin then terminated into whatever board is in the cabin. Usually the board in the cabin has a 30mA rcd up front as main switch, I then bond everything back to my DB in the cabin i.e water, gas, steelwork etc, as the 25mm CPC in the swa is sufficient to carry any fault current back to the main intake un the school and de-energise the supply.

For TN-C-S, I do turn them into TT installations i.e 25mm2c and drop a 25mm earth down to my rod, the rest is the same.

Hope this helps.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Rcd
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
lamb.a,
Last reply from
Mac,
Replies
6
Views
1,702

Advert

Back
Top