If it weren't for encouraging the un initiated I think I'd start an idiots guide thread
No offence Dave1064 sound like you are a have a go hero so 2 things here either get an electrician or if you have test equipment then get testing
Why do so many people just assume that an rcd or mcb must be faulty if it trips? Why not assume its doing its job and operating due to a fault?
I'm interested to know how many faulty rcd's people on here have found?
Tested all circuits All test out perfectly. Found fault. Due to a blown transformer in a elv fan. RCD picking it up where testing did not.
Maybe not so easy on functional test, if the fault was neutral to earth and the fan was on its own separate switch for instance. But IR test for sure
Why do so many people just assume that an rcd or mcb must be faulty if it trips? Why not assume its doing its job and operating due to a fault?
I'm interested to know how many faulty rcd's people on here have found?
Good point but dropping out each circuit from the dist board even before testing would have given big clues and would have expected to have done all the options above as an electrician before even contemplating posting a thread on it... in doing so it shows a lack of competence IMHO.