Re: 12Kw Electric Flow Boiler
Hi there.
All the ground source heat pumps I've done in the past for Nu-Heat, have been manufactured by a company called - Ice Energy.
I have to say they are really quite simple to install depending on wether its running central heating (radiators) and hot water or underfloor and hot water.
The biggest problem you're likely to have is providing the supply to the heat pump itself as it is usually a minimum of 63A for single phase i.e 16mm t+e plus 10mm earth run as a seperate sub-main and not from any other c.u.
Three phase is different, i.e easier to split the load over the three phases hence smaller rated supply but possibly in s.w.a.
The only control wiring that needs installing before you actually connect up is
1. outdoor sensor (should be on North facing aspect) - 3core cable I used arctic grade 3 core flex.
2. room sensor - 5 core cable I used standard 5 core flex usually in hallway away from heat sources (radiators) etc
3.You may (depending on system) have a 3 port zone valve to wire back to heat pump - 6 cores required, 2x3core flexes (Heat resistant)
4. Circulating pump - 3 core heat resistant flex
All other control wiring can be done before switch on as its in or next to the heat pump - flow sensors, thermostats etc. Best to check with heating engineer about positions of valves, pumps etc also type of system i.e rads/underfloor
If underfloor then you will have a seperate manifold which will need supply to activate zone controllers and possibly another circulating pump. This would be sepearte from heat pump though and could be run as a 16A radial from any c.u. It should come with it's own control box.
Hope this helps, If you need anything else just ask.
Cheers
Sorry to jump on this thread but as we are discussing boilers.Has anyone wired up any Nu Heat specifically "energy master thermal store cylinder with ground source heat pump ". I am just trying to get my head round it got the plans and relevant info .Has 12kw and recommends a 50 amp mcb but where is this fed to the heat pump itself and there are also fused spurs for the elements and pumps .(with me so far)and manifolds .would these be run separately on radials or all off the 50amp s will ring tech support in the week i am just trying to envisage the finished article so as not to miss anything out .Any help appreciated Scott
Hi there.
All the ground source heat pumps I've done in the past for Nu-Heat, have been manufactured by a company called - Ice Energy.
I have to say they are really quite simple to install depending on wether its running central heating (radiators) and hot water or underfloor and hot water.
The biggest problem you're likely to have is providing the supply to the heat pump itself as it is usually a minimum of 63A for single phase i.e 16mm t+e plus 10mm earth run as a seperate sub-main and not from any other c.u.
Three phase is different, i.e easier to split the load over the three phases hence smaller rated supply but possibly in s.w.a.
The only control wiring that needs installing before you actually connect up is
1. outdoor sensor (should be on North facing aspect) - 3core cable I used arctic grade 3 core flex.
2. room sensor - 5 core cable I used standard 5 core flex usually in hallway away from heat sources (radiators) etc
3.You may (depending on system) have a 3 port zone valve to wire back to heat pump - 6 cores required, 2x3core flexes (Heat resistant)
4. Circulating pump - 3 core heat resistant flex
All other control wiring can be done before switch on as its in or next to the heat pump - flow sensors, thermostats etc. Best to check with heating engineer about positions of valves, pumps etc also type of system i.e rads/underfloor
If underfloor then you will have a seperate manifold which will need supply to activate zone controllers and possibly another circulating pump. This would be sepearte from heat pump though and could be run as a 16A radial from any c.u. It should come with it's own control box.
Hope this helps, If you need anything else just ask.
Cheers

n my legend and plans it says low voltage screened do they mean heat resistant also its a new build thats why im eager to get it right .The mains is in one corner of garage heat pump in the other i was going to run heat pump off 50 amp cb as it only takes 43 amp its the 1140 ground source heatpump .Diolch Iechyd da