Work live on these all the time. Only bummer is when you take the cover off, and it's got new Schneider RCBO's fitted, the buttons always catch and you end up tripping something.
 
Merlin Gerin ISOBAR board anybody?

Work live on these all the time. Only bummer is when you take the cover off, and it's got new Schneider RCBO's fitted, the buttons always catch and you end up tripping something.

Agree about the Schneider RCBO's! Not so sure the isobar boards are any better than anything else when you drill a 20mm hole into them and the hot disc of metal drops out of the hole cutter into the mass of live wiring in the board!! :)
 
Here's what hse have to say on circumstances in which live working can be justified.

209 The factors which would be considered in deciding whether it was justifiablefor work to proceed with the conductors live would include the following:

(a) when it is not practicable to carry out the work with the conductors dead, egwhere for the purposes of testing it is necessary for the conductors to be live;

(b) the creation of other hazards, by making the conductors dead, such as toother users of the system, or for continuously operating process plants etc;

(c) the need to comply with other statutory requirements;

(d) the level of risk involved in working live and the effectiveness of theprecautions available set against economic need to perform that work.

In this situation section (d) may well apply, assuming the risk can be mitigated sufficiently, and the electrician involved was competent to work live. Though out of hours working would probably be the preferred way of doing it.

And some further guidance on the need to work live, and precautions to be taken when doing so.

(b) The need to be near uninsulated live conductors210 People at work are permitted to be near live conductors only if this isreasonable in all the circumstances. If, for example, it would be reasonable for thework to be carried out at a safe distance from the conductors then it would beprohibited for that work to be done near the conductors.211 People whose presence near the live conductors is not necessary should notbe so near the conductors that they are at risk of injury.(c) The need to take precautions to prevent injury212 The precautions necessary to comply with regulation 14(c) need to becommensurate with the risk.213 The system of work should: allow only people who are competent to do so towork on or near exposed, live conductors (competence for these and otherpurposes is further dealt with at regulation 16); indicate within what limits the workis to be attempted; indicate what levels of competence apply to each category ofsuch work; and incorporate procedures under which the person attempting thework will report back if the limits specified in the system are likely to be exceeded.This usually requires detailed planning before the work is started.

214 Suitable precautions should include as appropriate:
(a) the use of people who are properly trained and competent to work on liveequipment safely (see also regulation 16);
(b) the provision of adequate information to the person carrying out the workabout the live conductors involved, the associated electrical system and theforeseeable risks;
(c) the use of suitable tools, including insulated tools, equipment and protectiveclothing (see also regulation 4(4));
(d) the use of suitable insulated barriers or screens (see also regulation 4(4));
(e) the use of suitable instruments and test probes;
(f) accompaniment by another person or people if the presence of such personor people could contribute significantly to ensuring that injury is prevented;
(g) the restriction of routine live test work (for example product testing) to specificareas and the use of special precautions within those areas such as isolatedpower supplies, non-conducting locations etc;
(h) effective control of any area where there is danger from live conductors.

So HSE don't outright prohibit live working.

http://www.hse.gov.uk/pubns/priced/hsr25.pdf
 
Merlin Gerin ISOBAR board anybody?

Work live on these all the time. Only bummer is when you take the cover off, and it's got new Schneider RCBO's fitted, the buttons always catch and you end up tripping something.

Agree about the Schneider RCBO's! Not so sure the isobar boards are any better than anything else when you drill a 20mm hole into them and the hot disc of metal drops out of the hole cutter into the mass of live wiring in the board!! :)

True, plus the hot swarfe and cutting fluid. Depending on how the looms are dressed in the board, normally put a steel plate in to catch or let it run out.

Just to note we always have two men when doing this.
 
As a matter of interest... What did it feel like? Tingle? massive shock? Somewhere in between?

Well, as a matter of fact it started off with a few moans and squeals and then she really got into her stride ......whoops, wrong thread !

No but seriously... Electrical potential usually stays constant for different voltage levels; your resistance to earth or ground potential does not. So touching a live terminal conductor may cause a tingle, a shock, a stunning sensation, a powerful kick or boil your brains, dependent on the voltage level of the supply.

Anything above 50V ac will be noticeable, 18-25V if your heart is across your top and bottom appendages, but then touch the same terminal just after getting out of a bath or shower. If you are standing on an insulated surface you may only receive a micro shock, but then touch a metal appliance (exposed conductive part) simultaneously with the terminal and then 50V may feel a bit more like a Donkey kick.

The EAWR is pretty specific about working live and if there is no option because it would produce a greater danger when the power is off then you should follow a prescribed assessment of the risks involved.

Lots of the older sparks do the rub test, back of the hand brushed against an unknown conductor or terminal and survive (high body resistance - calloused hands and fingers). I personally don't recommend it as a method of determining the state of play with conductors and terminations.

Again, I don't agree that electricians should work on live switchgear due to other environmental factors such as disturbing dust and debree. There have been several explosions in the past when the dust has been ignited by the drilling within a cabinet.
 
What a load of crock...
i can't believe how many people here are afraid of working live!
Call yourself electricians? ....
yes, take all the precautions necessary to reduce the risk of danger, but at the end of the day if you want to be good at your job you have to take risks...
I'll continue to work live as I've always done, get the job done and get home...., the rest of you continue to cause your clients disruption, inconvenience and work evenings and weekends if you have too!
What next, should there be laws against the armed forces using live bullets in war? Should the fire service not attend fires in case they get burnt. Perhaps our kids shouldn't cross the road because of the danger...
Ridiculous.... No wonder this country and profession is in a state ....
 
Last edited by a moderator:
What a load of crock...
i can't believe how many people here are afraid of working live!
Call yourself electricians? ....
yes, take all the precautions necessary to reduce the risk of danger, but at the end of the day if you want to be good at your job you have to take risks...
I'll continue to work live as I've always done, get the job done and get home...., the rest of you continue to cause your clients disruption, inconvenience and work evenings and weekends if you have too!
What next, should there be laws against the armed forces using live bullets in war? Should the fire service not attend fires in case they get burnt. Perhaps our kids shouldn't cross the road because of the danger...
Ridiculous.... No wonder this country and profession is in a state ....

Lol.....Yes we all know the dangers of electrical potential energy but there are some simple souls out there who are either too dumb or damaged to know the difference between a calculated risk and cavalier behavior.
 
What a load of crock...
i can't believe how many people here are afraid of working live!
Call yourself electricians? ....
yes, take all the precautions necessary to reduce the risk of danger, but at the end of the day if you want to be good at your job you have to take risks...
I'll continue to work live as I've always done, get the job done and get home...., the rest of you continue to cause your clients disruption, inconvenience and work evenings and weekends if you have too!
What next, should there be laws against the armed forces using live bullets in war? Should the fire service not attend fires in case they get burnt. Perhaps our kids shouldn't cross the road because of the danger...
Ridiculous.... No wonder this country and profession is in a state ....

We're not expressing a preference for not working live at all, but you are just reading what you want to. Read the Daily mail much?

The fact is, it doesn't really matter what you think there should be laws against, but the law against working live just because you can pee higher up the wall than anyone else already does exist, whether you want it to or not. It's worth bearing in mind why health and safety law exists. It's because the very clients you worry so much about inconveniencing wwere, in the past, the same kind of emploeyr who didn't give a damn about their workers' safety. As for your stupid analogies about the militray and fire services, I'll treat them with the contempt they deserve. By the way, the Fire Services apply some pretty stringent safety precautions, and that wouldn't happen without law. Oh, and the reason being a soldier is so dangerous is because those charged with responsible use of armed services ofetn just ignore law and send them wherever osme political kudos (and a nice profit for the defence industries) can be made.
 
there is very little valid and legal reason why anyone should work live. (live testing is usually done under careful procedures with p.p.e. if required) for example medical facilities/ surgical suites!

working live is generally a prohibited action and highly frowned upon!
most consumers do not understand this and they simply don't understand the dangers involved!
I would simply ask them which would be more expensive the power outage or a wrongful death lawsuit the family could file against them?
 