I am doing a rewire in a Victorian house with split floor levels:

Basement
Lower Ground Floor
Upper Ground Floor
Lower First Floor
Upper First Floor
Second Floor

I have a limited amount of space to install the CU and cant fit anything bigger than a 16 module board (so have opted for a main switch and up to 14 ways for RCBOs arrangement). The Basement is being rewired by another contractor (as it is being completely renovated and the builder brought his own spark) and he needs three ways, which leaves me with 11. It is possible to provide separate power and lighting circuits for every sub-floor but it would leave the CU with no spare ways for future additions e.g.

Lower Ground Floor - 3 circuits (oven, ring final, lights)
Upper Ground Floor - 2 circuits (sockets, lights)
Lower First Floor - 2 circuits (sockets, lights)
Upper First Floor - 2 circuits (sockets, lights)
Second Floor - 2 circuits (sockets, lights)

Can any of you see any reason regs wise (I've calculated demand and its fine) why I couldn't merge some of these so the circuits are as follows:

circuit 1: oven
circuit 2: ring final lower ground floor
circuit 3: sockets upper ground and upper first floor
circuit 4: sockets lower first and second floor
circuit 5: lights lower ground and lower first floor
circuit 6: lights upper ground floor
circuit 7: lights upper first floor
circuit 8: lights upper second floor

I can't see a problem with it regarding division of circuits but as I've not done it this way before thought I'd open it up to you lot for some (hopefully) constructive criticism.

Thanks
 
If you are going down the RCBO route then "doubling" up some of the lights may make sense. I would make sure there are separate ways left.

Why does the basement need 3 circuits?
 
Understood about basement ...
If that's all you've got, I might be tempted to reduce lights by 1 and increase outlet cct by 1.
 
If you are going down the RCBO route then "doubling" up some of the lights may make sense. I would make sure there are separate ways left.

Why does the basement need 3 circuits?

Because its going to be a sort of granny flat. Still part of the main dwelling but with its own kitchen and bathroom. Although the best scenario would be separate CUs the customer is quite insistent that he doesn't want this and I cant see anything regs wise that says he absolutely has to in this scenario.
 
Why not just do upper and lower ground floor as 1 circuit, upper and lower 1st floor as 1 circuit and second floor as 1 circuit instead of splitting between ground floor and 1st floor upper and lower.
 
If the granny "flat" has a separate entrance then I would TELL the client that it needs its own CU.... that would give you 2 or 3 more circuits..
 
If the CU is in the granny flat, and the occupants of the rest of the property cannot ordinarily access it, I believe that might breach 537.1.4 "A main linked switch or linked circuit breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation".

No access to the flat = no ability to isolate under fault conditions... and of course no access to reset the protective devices for the other parts of the property.
 
Understood about basement ...
If that's all you've got, I might be tempted to reduce lights by 1 and increase outlet cct by 1.

Yes that might be better, how about:

circuit 1: oven
circuit 2: ring final lower ground floor
circuit 3: sockets upper ground floor
circuit 4: sockets upper first floor
circuit 5: sockets lower first and second floor
circuit 6: lights lower ground and lower first floor
circuit 7: lights upper ground and second floor
circuit 8: lights upper first floor
 
If the granny "flat" has a separate entrance then I would TELL the client that it needs its own CU.... that would give you 2 or 3 more circuits..

I might try and push a bit more on this, but even with its own entrance I think it can still be classed as an annex rather than a separate dwelling (assuming that was your reasoning for it being absolutely necessary, but please correct me if I'm wrong because if there is something official I can use to make the point I will).
 
If the granny "flat" has a separate entrance then I would TELL the client that it needs its own CU.... that would give you 2 or 3 more circuits..
If the CU is in the granny flat, and the occupants of the rest of the property cannot ordinarily access it, I believe that might breach 537.1.4 "A main linked switch or linked circuit breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation".

No access to the flat = no ability to isolate under fault conditions... and of course no access to reset the protective devices for the other parts of the property.

Even if the basement is rented out as the landlord he can gain access immediately if it is an emergency (see here), though I'm not sure what that would cover. I agree that for isolation purposes it would be better to have a CU in the main part of the property and I'll have another go at persuading the guy but its not completely clear cut and I don't want to lose a £6,000 job if I can help it. Although if there is some specific official guidance that covers this and insists on a separate CU I will of course insist on it, regardless of his response.
 