Evening all. The OSG says "As a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring.".

Okay, so what is the maximum length for a fused spur then? I don't seem to be able to find the answer in the OSG or BBB. I assume the limiting factor is voltage drop, but how is this determined?
 
I think we're driving down the wrong road here Charlie. The OSG states that 1/8th rule is for unfused spurs, I want to know the max length of fused spurs. I assume there is a difference, otherwise why would the OSG say 'unfused spurs' rather than just 'spurs'?
 
Ahh sorry didn’t realise you mentioned fused spurs..
Yes as you say it would be down to volt drop for the length of the cable and current
 
That's the problem, determining the volt drop for a spur from a ring. How do you do it? Calculating the voltage drop for the spur bit I can do, but not sure about the ring part.
 
That must be total length of cable then. But for sure the OSG also states an A1 RFC is maximum 100sqm floor space.

For a 100sqm room you could be using any length of cable from 20m to over 100m in length, dependant on the route the cable takes etc.
 
for VD on a spur, I'd estimate the length of cable from one end of the rfc and add the spur length, then use mV/A/m. this would give a pessimistic figure as the VD on the rfc part would be less.
 

Reply to Ring finals and fused spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K
Just a quick question from a new qualified sparky. So in 433.1.204 when it says the Iz of the cable must not be less than 20A for a ring final...
Replies
16
Views
3K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Evening all. Your thoughts please: I was helping out another spark today. The job was to spur from a ring final to a 13A fused spur, to feed...
Replies
27
Views
9K
Hi all, Planning on wiring my neighbour's summer house which will be 15 metres away from the end of the house (20-25 metres total distance from...
Replies
29
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock