Discuss Ring main r1+r2 reading really low - 0.01? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
tomodo
hi guys just wired up a new ring main for a house, confused on the test results though, firstly all other ring mains in the house that are new are okay and have came out as expected, tester has just been calibrated and batterys are okay and the ring main is a true ring... am using a metrel tester with the easy switch adaptor and have connected up right for testing at board.
Results for dodgy ring main are as follows
L-L 0.80 ohms
N-N 0.81 ohms
E-E 1.25 ohms
R1+rn 0.52 ohms
R1 + R2 0.01 ohms
Does anybody have any ideas why the r1+r2 reading is so low? I have read else where it could be to do with the metal backboxes being bonded making a parrellel path is this common?
Cheers for reading be grateful for any replys
I suspect you have a short between line and CPC.
Do a quick IR test... L-N, L-E, N-E... I think you'll get good readings for L-N and N-E and a very poor result for L-E.
To find it, try linking line and CPC at the board on one leg only... Test the outlets and record the results. The further you get from the board, the results should go up, increasing the further you get from the board. If you find they go up and then down... check the accessories with the lowest values as there's likely to be a short in the back box or on the leg of cable between the two with the lowest values.
I have an easi switch, but gave up using it a long time ago .....
Are you 100 % sure you connected it all correctly to the 6 ends?
Hi bud,have you done any other testing,apart from at the board?
...It is also only a matter of time,before the terminology police begin r1r2/R1R2 questioning...;)
With a reading of 0.01 ohms it would be less than a meter away if using 2.5/1.5.
R1+R2 of 2.5/1.5 is 0.019 per meter.
I tripled doubled checked i had it connected right! But thanks i will try that tomorrow, l-e did have a lower IR at 500v then n-e and l-n it was around 100M ohms though so well in allowance but normally i would expect over 999Mohm could the 100Mohms be low enough to be giving me the bad r1r2 readings? And also circuit works fine live?
And 123 the easy switch is from metrel does all your ring main tests in one go without having to mess about with connector blocks , not sure if id reccomend though yet
I will let you know the outcome
had a similar scenario a while back when replacing a part of a damaged RFC, the electrician who did the original install had twisted the 2 cpc's together in the back of the consumer unit, they were then separated out and sleeved to the earth bar in the CU, so at first glance appeared separate, it caused a little confusion at first, as soon as i untwisted the wires so they were not touching, I got sensible results.
Reply to Ring main r1+r2 reading really low - 0.01? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...