Guys, I generally have had a pretty narrow industrial focus and have recently branched out into domestic and commercial and have come across a situation that just doesn't feel right. I have been asked to do an EICR at a commercial property (listed building) where a known defect is that one of the lighting circuits has no CPC and I have had a quick look and agreed that this can be resolved. However whilst I was running around looking at this problem I noticed that the building has a metal internal roof. It kind of looks like the inside of a nissan hut, with sheets of curved galvanised corrugated metal bolted together and (I assume to something above). However, there is no continuity between the roof and the main earth. Is this permissible in the view of you guys?
 
IR test from steel roof to MET. if it reads > 22 K ohms, then it's not extraneous and does not require bonding.
 
If there is any electrical equipment mounted to it or cables passing through it, it may need bonding! Otherwise as Tel.
 
but nissans are insulated from earth by the tyres.:24:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Roof Earthing
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
Is it live?,
Last reply from
SirKit Breaker,
Replies
6
Views
1,867

Advert

Back
Top