Discuss Running outside lighting cables in render in the UK Electrical Forum area at ElectriciansForums.net

Stubby

-
Reaction score
2
Hello,
I'm looking to extend my lighting circuit outside of my house before I have the house re-rendered. some of the wiring routes will need to go up and over windows etc so some of the cable routes will be outside the permitted cable zones. I was planning to chase t/e into the wall and to protect the cable with the galvanised steel channel in the places where the cable is outside the zones. my question is, is an acceptable method of protection? Any help or guidance would be appreciated.
 
Just thinking out of the box. What about running the cable within 150mm of soffit and drop down to light? May be not possible if it is a double story wall but if it is a single story wall, maybe that could work? Personally not done this way and would rather run inside and come out to light. But if customers don't want internal work, maybe the way I stated could be possible?
Don't use t&e outside like tel has said.
 
Thanks for the comments. Running cables inside is not possible as all the interior is finished to a high standard and I cant see a neat way of getting the cables routed. Unfortunately I cant go up to the soffits as it is a double storey property. Does the 150mm rule apply to around window surrounds?
Cheers.
 
Thanks for the comments. Running cables inside is not possible as all the interior is finished to a high standard and I cant see a neat way of getting the cables routed. Unfortunately I cant go up to the soffits as it is a double storey property. Does the 150mm rule apply to around window surrounds?
Cheers.
Why not refer to your copy of Bs7671?
 

Reply to Running outside lighting cables in render in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
553
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock