What do you mean no main earth conductor?What code would you give for a Swa supply 3p/N,95mm.
Supplies remote school block,2 storey,no main earth conductor,using sheath,the main earth bonding originates from this Swa,for this block,@ Main Panel board,& is 16 mm
The main earth @ origin is 120mm,Main bonding 50mm.
Cheers
Your opinion is flawed unless inspection and testing revel otherwise.Correct a cpc,my opinion is a code 2.
A main earth should have been installed with this Swa,to provide an adequate earth,& Main earth bonding.
Ha ha,someone’s got itTN-C-S.
I mean you can’t go on opinion, only by proof that it is potentially dangerousYea it’s a cpc the Swa is being used for Main Earth @ the Main Panel in the block.
It’s also being used for the Main earth bonding conductor.
The situation is not potentially dangerous,what are you going on about my opinion is flawed,
The earthing is Pme Tncs.
But if you believe it’s not potentially dangerous how can you then code 2 it?Ok,it’s been in place since early 70’s,so no it’s not potentially dangerous.
The nitty gritty here is,the sub main to the block.
My opinion is it’s not correctly installed.
The cpc would be ok in protecting the Swa,but not ok to support Main earth bonding.
Code 2
Reasoning cable not sized,to accommodate main earth bonding.But if you believe it’s not potentially dangerous how can you then code 2 it?