I am guessing the OP is concerned more so about equipotential bonding in the block as this will need to meet the requirements of the size and nature of the supply and if my brain serves me correctly :rolleyes:, you cannot utilise the SWA sheath to satisfy this, it would need to be a dedicated core or a seperate conductor.... this is all assuming that equipotential bonding is required in the block itself?

It doesn't help and only confuses matters when you get muddled up with your terminology of how you describe the layout - it is a sub-main therefore using the term 'main earth' is incorrect as that is your primary earth conductor at the origin.
 
The PEN conductor and not the main tails would need to be 150mm or above for a requirement of a 50mm copper bonding conductor, so despite the fact it’s 50 mm in the main building could be down to an over specced original design and it maybe even larger than what is required.
It’s the PEN conductor which determines the required size of your bonding conductor however it’s most probably correct that your swa armour is going to be well undersized.
Sometimes you just have to assume it was designed correctly if you have no original design information, the existing building I mean and not the added block.
 
As above - you need to verify the requirements of the install and confirm them for us before we can comment, where required to be 50mm the equipotential bonding is there for safety reasons and is sized so to deal with network faults when associated with TNC based supplies, for example the N/E sheath of a PEN conductor suffers corrosion, this can lead to high resistance or even broken Neutral which can lead to high currents finding alternative paths through local installations.

EDIT- in answer, the SWA armour will probably be able to handle such a situation as it meets CSA compliance but falls short of regulations, this thus is not a safety issue but more so a compliance breach.
 
This only goes up to 70mm,,Main bonding over that is 50mm
 

Attachments

  • DC428654-85F5-4DEA-B46B-6DFDD73F0D93.png
    DC428654-85F5-4DEA-B46B-6DFDD73F0D93.png
    19.4 KB · Views: 58
The PEN conductor and not the main tails would need to be 150mm or above for a requirement of a 50mm copper bonding conductor, so despite the fact it’s 50 mm in the main building could be down to an over specced original design and it maybe even larger than what is required.
It’s the PEN conductor which determines the required size of your bonding conductor however it’s most probably correct that your swa armour is going to be well undersized.
Sometimes you just have to assume it was designed correctly if you have no original design information, the existing building I mean and not the added block.
Thanks,agree on that, so a code 2 regarding undersizing of earth bonding cable
 
My opinion is on this Eicr,regarding all above,I believe the sheath of the Swa maybe appropriate for use as a cpc.
The main bonding is the issue & will not comply code 2
 
This only goes up to 70mm,,Main bonding over that is 50mm
Not sure what that’s off but bonding on a pme arrangement has nothing to do with the csa of the line or neutral conductors in the consumers side, it’s the DNO PEN conductor csa you need plus the DNO May stipulate a csa regardless
 
Yea ok,not got the exact Eon supply conductors,will try & source that.
Saying that the earth bond conductors already installed in the main block are 50 mm.
 
You really need to use the correct terminology when discussing or asking questions about this sort of thing.
Talking about main earth's and using an SWA sheath as cpc makes it appear confusing or that you don't know what you are talking about.

The SWA sheath is made of plastic, it's the armour which is under the sheath which can be used as a protective conductor.

Mixing up terms like CPC, main bond, main earth etc confuses the issue a lot.
 
It is almost certain the armour will not be able to support bonding given the possible supply PEN size.
 
You really need to use the correct terminology when discussing or asking questions about this sort of thing.
Talking about main earth's and using an SWA sheath as cpc makes it appear confusing or that you don't know what you are talking about.

The SWA sheath is made of plastic, it's the armour which is under the sheath which can be used as a protective conductor.

Mixing up terms like CPC, main bond, main earth etc confuses the issue a lot.
Agree,my wording may not be 100%,I know the armouring can be used for cpc,Main earth terminology was incorrect,to ask if I know what I’m talking about,seems a bit rude,but hey oh,have a good bank holiday.
 