cliffed

-
Arms
Would you divide the 5.13 ohms by 4.
I personally don’t think so.
Also the R1 /Rn short circuit resistances are different from the usual R1 /R2 measurements.
Found those in an electrical book by,that man.
The Zs on this circuitB4707BB1-51E7-4A35-98FA-BA188A64EA04.jpeg was above the permitted figure,so just had a play around to see if this complies,anyone agree.
 
t=K2S2/I2 is the formula to use.
Nothing to do with a high earth fault loop impedance as the line to neutral loop measured loop could be significantly lower.

t being the maximum time in seconds allowed before damage to the live conductors and surrounding insulation occurs.
so does your short circuit fault current disconnect before damage to the live conductors only occur?
 
Upvote 0

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Short circuit compliance on high Zs readings
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
Ian1981,
Replies
2
Views
1,494

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top