Hello All

Ive got to fit a new shower in a commicial building our company look after. I think the shower is supplied from a type c 50A MCB MEM mem sheild board. What i was thinking was replacing this with a type c 50Amp 30mA RCBO.

Also would the max Zs for this RCBO still be 0.46 ohm as in the BGB pg 56 table 41.3

Thanks

James
 
Thanks

Just looked at it table 41.5 30mA 1667 ohms would a minor works cert be ok. iam i right in choosing a 50A Type C RCBO as 10.8KW pulls 47.0A but then will the shower run full bore.
 
50A MCB = 10mm cable ( but you knew that anyway).
 
Thanks

Just looked at it table 41.5 30mA 1667 ohms would a minor works cert be ok Technically if your changing the circuits protective device you should issue an EIC.

iam i right in choosing a 50A Type C RCBO as 10.8KW pulls 47.0A but then will the shower run full bore. As you Zs will now be 1667 there is no problem using a C type RCBO, though there is no reason to go and purchase a C type with a shower, B is more than adequate.

........................
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower 10.8kw advice please
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
James Sutton,
Last reply from
James Sutton,
Replies
5
Views
1,599

Advert