Obviously depends on cable calcs, length of run, design current, presence of insulation and other de rating factors. 10mm is pretty easy as long as you dress it in tidy. Could do 2 6mm in parallel as long as they are run the same route same length but I wouldn't bother
Can't do 6mm and 2x 2.5 at all though.
2 x 6mm in parallel easier to connect than 1 x 10mm ? A parallel supply for a final circuit ? The mind boggles.
As gns says, 10mm is not that hard to manage, and if that's what the calcs say, that's the cable you use.
Its not about Cable Calcs.. im more talking about CROSS SECTION AREA
it DOSE say 10mm CSA .. what 2x6mm would be 12mm CSA ..
Thats a Darft Comment Flanders...
as for the 4x6mm to replace a 10mm .. i think you might of read things wrong there
It's not the daft really though is it? If you had two cables in parallel that would make 2 cables on the supply side of the switch/pull cord and two cables on the load side of the switch/pull cord making 4 cables.
But the comment Flanders made suggest putting 4x6mm Cables in one HOLE..
But at least the CSA would be ok.. im just shocked that some people dont see that 2x6mm CSA is 12mm CSA and would be, but BIGGER than a 10mm CSA.. I know i come from a Electronics buts basic.
I think I've said this before, but using 47mm deep backboxes helps, as does using a 2 gang (tall) switch if possible. As said, dress the cables well and arrange them carefully so there is room for them as you offer the switch to the box.
Point was that some guy on another forum had 6mm cable put in with 40A MCB that went in to the loft ..
Now with cable calcs that can drop to about 37A also the shower I think was 10K
He had a few electricians, in about it some say 6 and some say 10mm
As the 6mm was it might of been cheaper to put in a 4mm to make it up to 10mm CSA
The other thing was that lot of people didn't seem to understand that a 10mm CSA cable would be that same as 4x2.5mm CSA
What shocked me as I did think that kind of Maths was basic
Plus ten points for thinking outside the box. Minus thirty points for lack of understanding of the regulations and practicalities of installation.
The reason that paralell cables are commonly used in larger circuits is that the sum of the parts is greater than the whole. If you look at the current carrying capacity of cables you will see that when the csa doubles the ccc only increases by about half. This leads to a situation where, say, 1x 70mm 4core can be replaced by 2x 25mm 4core and still have the same ccc.
However there are special requirements for parallel cables in he regulations and you need to carefully consider the protection arrangements and ensuring correct current sharing between the cables.
It is forbidden to install different size cables in parallel or for the cables to be different lengths or follow different routes.
As for the 10KW shower on a 40A mcb, it should have a running current of 42A so should be on a 45A supply to start with, however as it is a fixed load you would calculate cable size based on 42A not the rating of the OCPD as overload protection is not required.
Omg so this guy who has a shower installed by and electrician with 6mm cable 40A MCB going via loft.. Is OK with you guys
Sorry I must be in the wrong forum my error minus another 60
Forums ain't for me, I can't read them and tones just don't work for me...
No-one in this thread has misunderstood the maths of doubling cables up. People are disputing the advantages and practicalities of doing it in this particular case. And you should not use paralleled cables of differing csa's or type. Daz
this makes me think i've gone all wrong with buying a toyota hiace van, when 2 astra vans in parallel would carry the same weight.
A 10mm^2 conductor wouldn't need 2 * 6mm^2 in parallel for equivalent current-carrying capacity - probably more like 2 * 4mm^2.
Really parallel conductors are far more appropriate for a distribution circuit than for a final circuit, so I wouldn't be advising that approach at all.
As for other suggestions made, you cannot parallel two different cross-sectional areas of cable together as the current flow wouldn't distribute evenly.
Reply to Shower Cable in the UK Electrical Forum area at ElectriciansForums.net
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...