B
Baker1988
hi all just a quick question my girlfriend dad has just had a shower fitted cos his old one has broke (just a like for like)it was just a friend of his who did it for him dont think he is a spark just had some experiance i have checked it at the request of my girlfriend as she does not trust her dads friend it all seems fine there is not test sheets with it so i did a few tests zs and ir and all seems fine the only problem i have got is that the board has no rcd it is a old board but not really old it has mcbs and even a few rcbos buti told him he should really have a rcd on the shower circuit but i would probily be easier to get a rcbo for the circuit but he does not want to shell out the £27 for it so my girlfriend said she will buy it if i think it needs it just so he is safe so what do you all think does it need one i think it does but thought i would ask you lot first
If thats his attitude then I probibly wouldn't bother. You've told him. He can't be bothered (and for the sake of £27!!!), why should you be!!
ours is on a dual pole RCD as per manufacturers instructions (ie not a single pole RCBO), fitted via a seperate garage unit set up on the circuit. I'd check the instructions, then it should be simple enough to convince anyone that it should be on an RCD.
Hi me my self I am not that bothered its my girlfriend who is a bit worried I have checked the manufacturers data and it says it should have a rcd fitted either on the whole installation or the individual circuit doesn't say any thing about a double pole rcd even though that is usually what they are I always thought on a rcbo that the neutral switched of any way as you put the neutral into the rcbo and then connect the rcbo wire to neutral
to do it right its a notify work ,need rcd ,you never said the size the shower or the cable ,plus you don't know how the cable run under the carpet !!!!!!
Interesting topic chaps.
Legally, replacing a like for like shower is not notifiable, nor do you need "quals".
However, if the manufacturers instructions state that it should be protected via RCD (which 99.9% now are), then this installation would be.
Hi yeah it is a few pints job and the cable is 10mm twin and cpc and a 8.5kw shower on a 40 amp mcb and the cable is eun in conduit up into the loft where it been layer over the top of the insulation then down into conduit down the cobard to the consumer unit so the run is fine I can see all of the cable I am not bothered about it I just would just like it to be safe for him
Hi so should I put a rcbo in as a rcd would be more messing about and cost
RCBO £20-£30 or the price of a life if someone dies? Some people are so short sighted. As others have said, you can take a horse to water...
The install as a maintenance replacement is OK, however in order to meet the current regulations a 30mA RCD is required for all circuits in a room containing a bath or shower.
In order to upgrade the circuit to current regulations then an RCD would be required and there is no doubt that this would make the installation safer.
However the current installation is no less safe than it was before the replacement shower was fitted.
I would fit an RCBO into the board for that circuit if one will fit(RCBOs do not switch the neutral, you need the neutral in the RCBO so that you are not connecting to the neutral bar and causing the RCBO to trip a la shared neutral).
But do you then RCBO the bathroom lighting circuit and the towel heater as well?
However if the owner does not want it there is nothing you can do, unless your girlfriend arranges it for you.
well no , youre not working on these circuits to replace a shower , nor are we obliged to bring the entire installation upto current standards when you're only working one 1 part of it.
but RB's comment on leaving the install no unsafer than before is bang on the money.
You do not have to RCD/RCBO any other circuits at all in the bathroom, only the one in question.
If the manufacturers instructions say that the shower must be protected via 30mA RCD, then this will override BS7671 etc.
This is a replacement, not a new install.
Edit: biff beat me to it! :D