B
bigbaddave
I have been called back to a job where the pull cord is yet again not working. This is the sencond time they have had this fault.. Take the fitting down and the whole inside is a melted mess.. Now the shower is a 8.5kw fed on 10mm twin and earth on a 32a mcb. Install method B,
I have tested R1 + R2 and then R1 + and both exactly the same 0.07 which would tie in with the cable run. This is tested to the shower through the pull cord. ZS at shower = 0.50 (Testing with Metrel and thats the lowest reading on Loop)
Now i put the first one down do naff fitting but now im not to sure.. Has anyone else has issues with this.
Any idears fella's ?
I have tested R1 + R2 and then R1 + and both exactly the same 0.07 which would tie in with the cable run. This is tested to the shower through the pull cord. ZS at shower = 0.50 (Testing with Metrel and thats the lowest reading on Loop)
Now i put the first one down do naff fitting but now im not to sure.. Has anyone else has issues with this.
Any idears fella's ?