Hello All

Was asked by a mate to take a look at his shower in a flat that he rents.

He is in the shower for around 10 mins the the 4OA mcb trips and gets a strong smell of burning.

I opened up the 45A DP pullcord everything was ok there all connections tight. It had what appeared to be a 10mm flat twin and earth(grey). Went down to the CU and there was a white cable. Further investigation found that in the loft space they had joined both cable using 32A connector block which was completed melted. I LOTO the shower circuit and said for him to contact his landlords.

Who does work like this its a shocker


JS
 
Can someone point me in the direction of the calcs in the regs for how far back you have to take the insulation to twist together 2 x 10mm cables????
Do you twist with the twist of the strands or against it? ???
Should I bend over the end of this mass of copper so no one hurts themselves on the sharp bits??????????
Could I get away with a reef knot as it looks neater?????
 
steve, if you want to bend over anything, i think you're on the wrong forum!
 
Have seen one running off the back of cooker switch as bathroom was above kitchen........

I bet its one of those 7 week qualified electricians.........
 
long as the tape is brown and blue........
 
GEDC4127.jpgHere one i found im sure i put this one up not looked round the house was a friends changed the CDU and when testing i spotted the shower but no circuit in the board for it , was wired off the ring main using terminal block under the floor ,its 1.5 3 core flex and im lead to belive it was installed last january by the local handy man !!!!!!!!!!
 
oh dear, he's omitted to fit the cable clamp . tut tut.
 

Similar threads

J
Replies
24
Views
3K
A
S
Replies
17
Views
3K
L
L
Replies
35
Views
8K
Australia
johnboy1963
J
S
Replies
11
Views
11K
B
Replies
26
Views
4K
Australia
GLENNSPARK
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower shocker
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
James Sutton,
Last reply from
telectrix,
Replies
30
Views
4,930

Advert