Hi guys,
Have an option of an old, but really solid superb condition and well made large +/- 200ltr compressor from Denmark. Rarely used since purchased/Build 1987.
Only supply I have is 230V Sing/Ph. Never had any dealings with 3 Ph.

First name plate.
Grundfos 3~MOT MG90LAR-24F115 No: 870000??
220 Δ/380 Y V 50hz 2855 /min
9.0 / 6.2 A IP 54 CL. F 2.2Kw
Cos 0.9 P1 - 3.0 Kw

Over a day searching and it appears there is no history on this now. Called people that were of no help on the plate details surprisingly. Suspect 220 delta 9.0A and P1-3.0 Kw relate to start up? Seeking confirmation and would be appreciated.

4mm2 supply +/-50M (pity not 6mm2) from main Cons box 32A MCB to 2nd Con Box with choice MCB and RCD. No other load.
At present to install this 3Ph with the 1Ph 230v I can only see a VFD as the option. If there are other options would be pleased to know. There are always unknown factors and losses with projects like this and hoping to hear those views of concern.
Compressor would be 3-4m from the Cons box and controller, if a safe and sensible solution ticks the boxes if and when it will be used, which will be little, not daily.
Thanks in advance.
 

telectrix

-
Mentor
Arms
Esteemed
think i paid around £100 for a 3 HP motor in a similar compressor.the original motor burnt out. the idiot who borrowed it ran it off a long extension lead and failed to see the motor had stalled due to volt drop. hence a dead motor.
 
  • Thread Starter Thread Starter
  • #5
think i paid around £100 for a 3 HP motor in a similar compressor.the original motor burnt out. the idiot who borrowed it ran it off a long extension lead and failed to see the motor had stalled due to volt drop. hence a dead motor.
This is a known issue to me, hence why I carefully explained without wanting to pretend I'm expert about cabling. This motor I saw a replacement online 3~ available £1,246 .... that is some dough:oops:.
Can see the build quality is very good, as most engineering was.
Best stick with it and find another way round it.🤞
 

Strima

-
Arms
Esteemed
You get a motor a lot cheaper than that. Madly enough I’ve found a few at car boot sales over the years but keep an eye on the usual suspects such as eBay and Facebook marketplace.
 
  • Thread Starter Thread Starter
  • #7
You get a motor a lot cheaper than that. Madly enough I’ve found a few at car boot sales over the years but keep an eye on the usual suspects such as eBay and Facebook marketplace.
Lucky I am not needing a new one, the one on it is fine, just wrong phase.
 

davesparks

-
Mentor
Arms
Esteemed
220/380 is not standard UK three phase so you won't be able to use an off the shelf phase converter.

I suspect you will need to go for a VFD to run this motor.
 
  • Thread Starter Thread Starter
  • #11
220/380 is not standard UK three phase so you won't be able to use an off the shelf phase converter.

I suspect you will need to go for a VFD to run this motor.
Thanks for the reply.
The compressor is in Spain and setup on 3~ which the owner had upgraded his place in the past. It originated in Denmark, although he was German. Since passed away.

Based on limited knowledge of VFD, it seems the correct rating is quite important to match, which may be different from the 2.2Kw on the motor. Perhaps contacting one of the suppliers will help?
 
There is a way of running a 3 phase motor with single phase using a capacitor.
 

ElectroChem

-
Arms
Thanks for the reply.
The compressor is in Spain and setup on 3~ which the owner had upgraded his place in the past. It originated in Denmark, although he was German. Since passed away.

Based on limited knowledge of VFD, it seems the correct rating is quite important to match, which may be different from the 2.2Kw on the motor. Perhaps contacting one of the suppliers will help?
The 220V 9A Delta from the nameplate is consistent with a 2.2kW motor. When running with a VFD it has to be at least equal in rating, and not too hugely over as VFDs are not designed to reliably protect motors much smaller than their rating from overcurrent.
If I had this compressor in front of me, I'd be perfectly happy to hook a 2.2kW drive up to the motor and press the go button.
 
  • Thread Starter Thread Starter
  • #15
The 220V 9A Delta from the nameplate is consistent with a 2.2kW motor. When running with a VFD it has to be at least equal in rating, and not too hugely over as VFDs are not designed to reliably protect motors much smaller than their rating from overcurrent.
If I had this compressor in front of me, I'd be perfectly happy to hook a 2.2kW drive up to the motor and press the go button.
Thanks for the reply.
I'd be happy to find a 2nd hand Rotary converter or VFD, but all about timing that appears.
It does look like a VFD is 6/4 Fav though. They are expensive, and must decide. I have looked at a few, avoiding e-bay and Amazon, just blatantly gear from China. Was tempted all but 30seconds. Invertek make them, I have an one on pool system, good gear but pricey.
Is there a make you might be able to suggest or know of that is decent. This compressor wont be used much.
Thanks again👍
 

Simon47

-
Arms
Esteemed
I'd have thought that it woukd run fine in delta. L & N to two terminals, cap between one of those and the other corner to assist the third phase. That is the basis of a rotary converter.
You'll probably want extra cap during start.

Having played with making a rotary converter in the past, look forward to a few blown fuses/tripped breaker while you work out the amount of cap needed.

It will help a lot if the compressor can be unloaded during start.
 

ElectroChem

-
Arms
Thanks for the reply.
I'd be happy to find a 2nd hand Rotary converter or VFD, but all about timing that appears.
It does look like a VFD is 6/4 Fav though. They are expensive, and must decide. I have looked at a few, avoiding e-bay and Amazon, just blatantly gear from China. Was tempted all but 30seconds. Invertek make them, I have an one on pool system, good gear but pricey.
Is there a make you might be able to suggest or know of that is decent. This compressor wont be used much.
Thanks again👍
I'd have thought that it woukd run fine in delta. L & N to two terminals, cap between one of those and the other corner to assist the third phase. That is the basis of a rotary converter. You'll probably want extra cap during start. Having played with making a rotary converter in the past, look forward to a few blown fuses/tripped breaker while you work out the amount of cap needed. It will help a lot if the compressor can be unloaded during start.
Using caps to make a pseudo-three phase supply is always a bodge. True single phase motors have their run winding designed to carry the full power of the motor, three phase motors are intended to carry a balanced load across the three windings.

I would also not use a cheap rotary converter, as these supply three lines at 0/90/180 not 0/120/240 phase angle so you still need to de-rate your motor. A compressor is exactly the wrong load for any kind of kludged up pretend three phase supply.

Use the right tool for the job, in this case that is a true 400V supply or rewire the motor to delta and use a 230V 1-to-3 phase VSD. Otherwise your next thread will be entitled "I blew up my compressor motor" :)
 
  • Thread Starter Thread Starter
  • #18
Using caps to make a pseudo-three phase supply is always a bodge. True single phase motors have their run winding designed to carry the full power of the motor, three phase motors are intended to carry a balanced load across the three windings.

I would also not use a cheap rotary converter, as these supply three lines at 0/90/180 not 0/120/240 phase angle so you still need to de-rate your motor. A compressor is exactly the wrong load for any kind of kludged up pretend three phase supply.

Use the right tool for the job, in this case that is a true 400V supply or rewire the motor to delta and use a 230V 1-to-3 phase VSD. Otherwise your next thread will be entitled "I blew up my compressor motor" :)
Thanks for the reply.
Yes Sir, I have seen a capacitor setup, but it was as an experiment and deemed not a good method.
Not clear on your last reply after your first an earlier one you confirmed you would be happy on this setup to go with a VFD.
Have you has second thought, or have I missed something there?
I had accepted using an Invertek, would be over £2-250. If this is not the tool for the job, I definitely would not spend that.
 

James

-
Mentor
Arms
Supporter
Esteemed
Use the right tool for the job, in this case that is a true 400V supply or rewire the motor to delta and use a 230V 1-to-3 phase VSD. Otherwise your next thread will be entitled "I blew up my compressor motor" :)
FVD & FSD are the same thing, variable frequency drive or variable speed drive.
that is the route i would be going down, wire the motor in delta and use a VSD.
 

davesparks

-
Mentor
Arms
Esteemed
Use the right tool for the job, in this case that is a true 400V supply or rewire the motor to delta and use a 230V 1-to-3 phase VSD. Otherwise your next thread will be entitled "I blew up my compressor motor" :)
A true 400V supply would be the wrong thing for this motor, as stated in the OP it is rated for 220V delta 380V star
 

Simon47

-
Arms
Esteemed
I would also not use a cheap rotary converter, as these supply three lines at 0/90/180 not 0/120/240 phase angle so you still need to de-rate your motor
Wouldn't 0/90/180 be harder to make than (at least an approximation of) 0/120/240 ? Reason I say that is that for a rotary machine, regular 3 phase stuff if common and cheap, to get 0/90/180 would need a custom wound machine. A static converter (i.e. a box with a few caps in it) will give you a 90° third phase - but only under no load - I have a Transwave example of that in the garage, and under load you can get quite a reasonable balance acroos the lines.
As I mentioned, a whike ago I was experimenting because we wanted a 3P supply for my mates home garage, partly to drive the 4 post lift we'd got hold of. Dad just happened to have a 5hp motor lying around which was going to be the basis of it - plus a few caps and an old rescued manual star-delta starter - the biggest probkem we had was getting it going ! I never finished it because my mate got divorced and the house got sold - so we no longer had a need for the 3P.
Sadly, that motor and the step up transformer were among the 400kg of motors I had to weigh in when dad died. If I'd had the room I'd have kept a lot of them.
 

ElectroChem

-
Arms
Wouldn't 0/90/180 be harder to make than (at least an approximation of) 0/120/240 ? Reason I say that is that for a rotary machine, regular 3 phase stuff if common and cheap, to get 0/90/180 would need a custom wound machine. A static converter (i.e. a box with a few caps in it) will give you a 90° third phase - but only under no load - I have a Transwave example of that in the garage, and under load you can get quite a reasonable balance acroos the lines.
As I mentioned, a whike ago I was experimenting because we wanted a 3P supply for my mates home garage, partly to drive the 4 post lift we'd got hold of. Dad just happened to have a 5hp motor lying around which was going to be the basis of it - plus a few caps and an old rescued manual star-delta starter - the biggest probkem we had was getting it going ! I never finished it because my mate got divorced and the house got sold - so we no longer had a need for the 3P.
Sadly, that motor and the step up transformer were among the 400kg of motors I had to weigh in when dad died. If I'd had the room I'd have kept a lot of them.
Yes and no. A full rotary converter that uses a single phase motor to drive a three phase generator will produce all the right angles and voltages. The cheap rotary converters use single phase with a cap to spin up a three phase motor, then tap the unused terminal for the third line. From my understanding, the magnetic interactions inside the motor produce a voltage at this terminal that is midway between the other two, which from a single phase source will give 0/90/180. The third line also has no guts and will sag under load, meaning this style of rotary converter can't drive heavy loads.
 

Simon47

-
Arms
Esteemed
The cheap rotary converters use single phase with a cap to spin up a three phase motor, then tap the unused terminal for the third line. From my understanding, the magnetic interactions inside the motor produce a voltage at this terminal that is midway between the other two, which from a single phase source will give 0/90/180. The third line also has no guts and will sag under load, meaning this style of rotary converter can't drive heavy loads.
No, I think you are misinformed there.
If you connect 1P across 2 phases of a 3P motor, give it a spin, and then apply power, you will get something resembling 3P out of the 3 terminals. It may not be too well balanced, but it will be something resembling 3P. It will do this without any caps, but adding caps will a) add a rotating element so you can actually start the converter, and b) assist in balancing the phases. As you say, without the caps, you have problems starting large loads, but once running these loads will add their own conversion.

One of the tales my late father used to tell was of a callout to a joiner's workshop - this was maaaaany years ago when he was an on the tools electrician. They had a problem with one machine - but only one machine. All the small machines were working fine, just this one big one wouldn't start. Turned out they'd lost a phase at the incoming mains, the machines running created enough of the missing phase for the smaller machines to start, but not enough to start the biggest machine. I guess they must have had something already running when the phase was lost, and that was able to start other machines.
 

ElectroChem

-
Arms
I'll freely admit that you all have more experience with rotary converters than myself, which would be none. One of the benefits of living in Australia is a very unified electrical system, and the regulatory backing to tell customers that no, we can't always 'just make it work'.
That said, I'd want to see a scope trace of a single phase driven rotary converter giving anything resembling a balanced phase angle output. When you're starting with two lines that are by definition opposite/180 apart, there's only so much you can do.
 
  • Thread Starter Thread Starter
  • #26
I'll freely admit that you all have more experience with rotary converters than myself, which would be none. One of the benefits of living in Australia is a very unified electrical system, and the regulatory backing to tell customers that no, we can't always 'just make it work'.
That said, I'd want to see a scope trace of a single phase driven rotary converter giving anything resembling a balanced phase angle output. When you're starting with two lines that are by definition opposite/180 apart, there's only so much you can do.
Well, I do feel a little better this was not something easy or common.
But then not received anything broadly recommended.
I will speak to Invertek tech guy and request what view he has on this situation a little more clearer if it's the only alternative.
Speed control is not a requirement.
However load might be an issue with a compressor when pressure drops and resumes under load.
 

Simon47

-
Arms
Esteemed
That said, I'd want to see a scope trace of a single phase driven rotary converter giving anything resembling a balanced phase angle output. When you're starting with two lines that are by definition opposite/180 apart, there's only so much you can do.
That's mostly the point of using a rotating machine as part of the converter - you have something capable of generating out of phase components relative to the input. I'm sure my late father could have explained it clearly - he used to design motors etc. for Brush back in the 60s - but my machines theory is rather scant.
I would imagine that if you take a standard 3P squirrel cage induction motor and apply 1P across two connections (with some current limiting !), then as you infer, without the rotor spinning then you'd simply get some variation on a single phase transformer. But once you spin up the rotor, with only one field present, the rotor is going to be going in and out of that field - rather than moving between fields as the fields rotate. That's going to create currents in the rotor cage, and the resulting field is bound to have some effect back into the field windings. As I say, my machine theory was never strong, and it's a lot of years since we did it at uni, but going on the principle of the current in coils trying to counteract change, I'd expect the currents in the rotor cage to act so as to try and reduce the variation in magnetic field as the rotor rotates. That's then going to induce currents in the stator windings with a similar relationship (magnitude and phase angle) to those you'd find if it was fed with "real" 3 phase.
So some of the 1 phase input current goes into creating rotor currents, and those rotor currents go into making 3 phase stators currents. Just how strong this is I don't know !
However load might be an issue with a compressor when pressure drops and resumes under load.
Compressors don't normally start under load. Small ones typically incorporate an unloading valve in the pressure switch that controls the motor - when the switch clicks over, as well as opening the electrical contacts, it opens a dump valve that unloads the pressure in the delivery pipe between compressor and reciever (there's a non-return valve that keeps the air in the receiver). Beyond that, there are various schemes for allowing the compressor to run up before getting onto full load - soft-start valves vent the air from the delivery pipe until it reaches a certain pressure, a dump valve may just allow the air out until some condition (may be just a simple timer) is hit, and there's probably other schemes I've never come across.
 
  • Thread Starter Thread Starter
  • #28
Appreciate all replies and contributions to an interesting topic. For me anyway. Contacted Invertek Tech man who was very patient and helpful. It does appear the VFD would be the best option for 230~1 to 230~3 and have a stable control. IP20 unit will be +/-£ 220 Which is a costly option. My moto is “Never buy Cheap, only good Value”. If anyone does know of a trusted lower cost option VFD that would run this compressor only on infrequent times on short time, please let me know. Thanks :)
 

James

-
Mentor
Arms
Supporter
Esteemed
I doubt you can do it properly for any less than that price.
 