Hi,

I've been digging and have nicked the outer sheathing of a 2.5mm SWA cable.
The protection and conductors are intact.

Would it please be possible to advise on how I can repair the outer sheathing by using heat shrink or any other suitable bonding agent to ensure no moisture flows in over time?

I will run an insulation resistance check before and after the repair.

Thanks
Kibz
 
If you’re absolutely sure there’s no damage to the inner cores, or the breaks in the armour strands, then wrap self-amalgamating tape around it.
It’s more waterproof than insulating tape.

For something that looks more professional… get an underground torpedo joint….
Don’t make a joint, but encase the damaged section within the torpedo and fill with resin as normal.

Have you got a photo? Some repairs are more suitable depending on severity of damage.
 
Hi Littlespark, Thats great thanks for your reply.

Where can I purchase the self-amalgamating tape and the torpedo joint kit from?
Attached are the pictures let me know what you think?
 

Attachments

  • 20220325_114936.jpg
    20220325_114936.jpg
    511.6 KB · Views: 133
  • 20220325_114944.jpg
    20220325_114944.jpg
    504 KB · Views: 150
  • 20220325_115005.jpg
    20220325_115005.jpg
    478.4 KB · Views: 162
I have never seen a swa cable with red bedding below the armour so I can only assume the bedding is also damaged and that red is conductor insulation. You are going to need professional help.
 
I hope that’s not a concentric, with the red core showing.
Could be a DNO job.

Slightly more mangled than I thought at first… a little bit of tape isn’t going to help.

Did you not see the yellow warning tape?
 
I hope that’s not a concentric, with the red core showing.
Could be a DNO job.

Slightly more mangled than I thought at first… a little bit of tape isn’t going to help.

Did you not see the yellow warning tape?
Think you may well be correct there.
 
  • Like
Reactions: Jim_e_Jib
Looks like concentric dont it.
 
  • Like
Reactions: Jim_e_Jib
Think you may well be correct there.
I’m not sure… certainly looks like a concentric, but the strands would be black??

Not entirely sure about that…
 
I’m not sure… certainly looks like a concentric, but the strands would be black??

Not entirely sure about that…
No I suspect you are correct mind you I can only find Chinese produced cables.
 
Last edited:
  • Like
Reactions: Jim_e_Jib
What depth was/is that cable at?
 
I’m not sure… certainly looks like a concentric, but the strands would be black??

Not entirely sure about that…
I have seen red strands.
 
I have seen red strands.
Red strands as the outer wires??

I thought red inner, black stranded then bare stranded…. Or split concentric with red inner, then black and some green on the outer
 
I thought the same but I'm swayed by fact he knows it's 2.5mm and says he can IR it, suggesting he has control of both ends of it.
The current IR results would be a good start.
 
Red strands as the outer wires??

I thought red inner, black stranded then bare stranded…. Or split concentric with red inner, then black and some green on the outer
Definitely seen blue strands brown solid core, sure I've seen red strands got me thinking now maybe not.?
 
Tried zooming in could be red conductor, good old 2 core SWA.
 
  • Like
Reactions: pc1966
It doesn’t look like like 2.5….

It needs professional repair, whatever it is.

If the OP could clarify when it gets looked at
 
  • Like
Reactions: Jim_e_Jib
Do we think the word 'slight' is underestimating things.
 
Yeah bit more than a nick more like a gash.
 
Hi All,

Thanks for all the comments. The cable was meant to be buried at 600mm but the person who laid in in that particular section skimped out at laid it at less than 300mm and the warning tape wasn't event 150mm above the SWA cable.

This cable has not yet been connected or energised so was able to check the ident. It is a 2.5mm SWA cable and was able to cut a small piece from the slack end. After the repair I will ensure the cable is installed to 600mm depth.

The pictures will illustrate the black sheath, the armour strands. You then have a red insulation inner sheath and then the individual 3 conductors Black, Grey & Brown).

This cable will be used for lighting only and the 2.5mm cable was chosen due to the long run of cable taking voltage drop into consideration.

Please let me know if the repair is still feasible?

Thank you all for your replies
 

Attachments

  • 20220325_151324.jpg
    20220325_151324.jpg
    375 KB · Views: 105
  • 20220325_151354.jpg
    20220325_151354.jpg
    284 KB · Views: 98
  • 20220325_151457.jpg
    20220325_151457.jpg
    213.5 KB · Views: 101
  • 20220325_151513.jpg
    20220325_151513.jpg
    322.9 KB · Views: 74
  • 20220325_151552.jpg
    20220325_151552.jpg
    313.6 KB · Views: 94
  • Informative
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Slight damage to SWA cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
Kibo_769,
Last reply from
philectrical,
Replies
31
Views
7,350

Advert