jordan123

I have a socket in a house showing up as live on both ring 1 and ring 2 ? powered up the house today and used a socket tester and it was flashing on both rings when I isolated each one on their individual MCB’s ? does anyone know what this could be ?
 
without further info, difficult. but seems like rings may have been interconnected by Dave DIY.
 
I have a socket in a house showing up as live on both ring 1 and ring 2 ? powered up the house today and used a socket tester and it was flashing on both rings when I isolated each one on their individual MCB’s ? does anyone know what this could be ?
Possibly a result of connecting it across two circuit breakers having failed to carry out initial verification before putting the installation into service. That would seem like the most likely explanation, although socket testers aren't necessarily hugely accurate but rather indicative.
 
Possibly a result of connecting it across two circuit breakers having failed to carry out initial verification before putting the installation into service. That would seem like the most likely explanation, although socket testers aren't necessarily hugely accurate but rather indicative.
The continuity was ok on ring 1 but not showing on the lives on ring 2 ? it’s very confusing . So I think the connection was ok
 
This requires further investigation from someone qualified as they will know the correct safe isolation procedures.
as mentioned buy others there is a chance that the rings are interconnected somewhere which makes this particularly dangerous when fault finding.
 
Last edited:
There is also the possibility of damage to cables,which could cause this - either way,it needs detailed investigation,in a methodical manner.
 
Is it possable one of the ciruits is tagged on with the ring.you never know.
 
Recently had a job where there is 3 rfc in the house and all 3 were interconnected. So in short no matter which 32a fuse you pulled all the sockets remained live.
I have temporarily put the entire lot onto one circuit to make isolation easier.
Going to be a right pig to sort out
 
  • Like
Reactions: DPG
each end of the ring is connectted to a different breaker,
if both of those breakers come from the same source ?
that would explain why he has gotten away with it !
But it is potentually dangerous and needs to be correctted.
This requires methodical thinking and testing
So best left to a good electrician.
 
Last edited by a moderator:
Sounds like the rings have been crossed. Good old dangerous diy
 
I have a socket in a house showing up as live on both ring 1 and ring 2 ? powered up the house today and used a socket tester and it was flashing on both rings when I isolated each one on their individual MCB’s ? does anyone know what this could be ?
It looks like the two ring circuits are crossed with one another,and the person who installed the rings did not verify ring continuity.
 
Need confirmation of 3 rings ,

Are they all 32A MCBs ?
(last years post - may not get to find out)
 
Is this a new years resolution to see how many old threads can be resurrected?
 
  • Funny
Reactions: DPG
Is this a new years resolution to see how many old threads can be resurrected?
if they don't take care they might even bring me back up from dead.
 
  • Funny
Reactions: ferg and DPG
There was a really old thread but I can’t find it now.
Something about replacing round pin plugs with fancy square pinned ones, and having a fuse actually inside the plug!!!!
New things. They’ll never catch on.
:p;)
 
  • Funny
Reactions: telectrix and DPG
Obviously, an interconnection with two COMPLETE rings would mean all the sockets live with either mcb. Sounds a bit more complicated than that though.
 
  • Like
Reactions: static zap

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Socket showing live on both ring mcb’s ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
jordan123,
Last reply from
ipf,
Replies
15
Views
2,724

Advert