Discuss split phase supply in the UK Electrical Forum area at ElectriciansForums.net
N
nobelz66
Hi guys ive just joined this forum so im hopeing for some help please
Ive just been asked to estimate a job basically to supply power to 15 new log cabins each requireing a 32a sp supply ,the existing park is supplied by a 3 wire split phase supply rated at 400A split also there is an existing 100a 3 phase board not fully loaded been run on a 4c 50mm2 swa and a 95mm2 cpc via a 200A panel board at mains position the L1 and L2 is supplied from one side of the split phase the other L3 connected to the other my question is as follows:
1 # do i calculate the new cable run as a 3 phase cable ie 4 c 120mm2 or calculate as a single phase which would make the cable 180mm2 min
2 # do i allow diversity on the log cabbins called niceic they said yes
any help would be very gratefull
First off, It's not a split phase supply, it's simply 2 phases and neutral. (Unless that supply is derived from a single phase 3 wire transformer, which i very much doubt!! lol!!!) Though why the park is being supplied with such a 2 Ph +N arrangement, only the original installer would know!!!
1/ ...Yes, as a multi phase supply.
2/ ...yes.
Why can it not be split phase eng ? Measure between phases if 0V single phase if 480V split phase or am I missing something. The rest I agree with.
From how I read the OP there is a smaller 3Ph available.
I’m totally confused as to why the DNO would make the 2
[SUP]nd[/SUP] supply either 2 or split phase.
I cant see how traditional 3P can be derived from a split phase supply???
Not my field, so possible nonsense alert.
I can't see how you can without the use of 'technology'.
Is a split phase supply derived from a centre tapped winding, like a tool tranny, phases 180[SUP]o[/SUP] apart?
Would be greatfull if someone could explain the split phase setup, compared to the 3 phase that im used to.. thx :)
Essentially, yes.
The Tx will have a single phase primary with the secondary centre tapped to provide 2 x single phases 180 apart with a shared neutral.
Measured at the building incommer between the two and you would read typically 480V.
Reply to split phase supply in the UK Electrical Forum area at ElectriciansForums.net
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Hello all Just doing some cable calcs for a shepards hut site, the site has an incoming supply of 2 x 250a single phase supplys, was hoping to...
Hi - first-time post from a complete novice. I want to install a 24kw electric boiler on my property but that size requires Phase 3 supply...