Always check the supply the amount of DP switches on these i have found faulty ,do an R1+R2 and and Rn + R2 at least you know the cables are ok but as telex has said thermostat , way to find if thats ok is to switch the isolator off and do a continuity test at the incomming cable terminal block ,also do an insulation test of the elements ,and do a proper continuity test of the elements and seee what the resistance is ,as doing a continuity with a set of prods may not be acurate