Discuss Strange bonding of gas question. in the Australia area at ElectriciansForums.net
K
KNIPEX
Hi guys, ive taken a main bond to the gas pipe which is in steel as its a commercial job, where it enters the property, which also has a gas shut off switch there. however the pipe then runs 15-20m inside the building where it connects into a gas meter still inside the building.
it then runs around the building from the otherside of the meter.
so really i have bonded the incoming not out going, its a strange one.
i was thinking of putting a link acoss both pipes just above the meter so the outgoing is bonded too.
what your views and advice on this please??
where practicable it should be bonded within 600mm of the meter outlet union.
i would take another bond to the outlet side of the meter and treat the incoming pipe as a seperate equipotential bond
Why would you do that.It should be bonded 600mm from the consumer side.Supplier side should be down to the gas company:p
yeh but the suppliers(its not really a suppliers side ) is still running through a building, and was carried out by the same contrator that did all gas work.
the other way to look at it, if there was no meter, you would bond it where it enters the building.
reg 544.1.2 is intresting regarding the above.
We are required to form an equipotential zone Within the property ..therefore any extraneous conductive parts are required to be bonded to the M.E.T.
The metallic pipework will therefore require bonding within 600mm of entering the building...i would also advise installing a bonding link acroos the meter...this bonding link is fairly common practice where water meters are installed within properties etc.
Regards....spark1
The bond should go as near as practical to the entry into the building ,but on the consumers side of the meter
The pipework that is prior to the meter and exposed in the building should be bonded across to the main gas bond
The reason for doing so is that the supply pipe may be altered in the future and the main gas bond would be still on the exposed internal pipe and no chance of a loss of main bonding continuity due to change of supply material l
thanks for the replies, have we got a definite answer though some say bond where it enters some say at the meter it really is a catch 22 :(
Hi.
I would run my main equipotential bond to within 600mm of the point of entry, then install a cross bond link at the meter between suppliers an consumers side. Have seen it done before and feel this is the way to go.
Cheers.
I would bond within 600mm of the consumers side of the meter, then link the gas pipe where it enters the building to the main steel structure of the building effectively equipitential bonding.
thanks guys, however the steelwork has a seperate bond to it already, so goes make to met so will be all at the same potential anyway. i think i will go on the idea bond 600mm where it enters the building and link at the meter, which means all the pipes are bonded not just the consumer side if i did it from the meter.
would dread to think what would happen if the pipe which is exposed 10-20m from point of entry became live and was not bonded.
Regards....spark1
I agree with spark1
Reply to Strange bonding of gas question. in the Australia area at ElectriciansForums.net
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...