Hello all.

Had a job today putting in a new kitchen circuit. Plan was to put in a new CU just for the kitchen sockets and lights. When I looked at the cut out, found a Seeboard PME label and the neutral came out of the cut-out into a Henley block then onwards to the meter. So far so good but the Henley block was also the MET and was connected to the incoming main by a ribbon cable TNS-wise. Never seen anything like this before and not sure how to treat it. Anyone ever seen this before? Photo attached.

Thanks.
View attachment 35883

View attachment 35878

View attachment 35879

View attachment 35880

View attachment 35881

View attachment 35882
 
It isn't uncommon to see this arrangement at least you have a notice stating the system type. Could do with just one earthing conductor from the service terminal block.
 