Marconi,

Have tried your steps. Unplugged dishwasher.

To complicate things even further in the middle of the night RCD tripped again. This time it could not be reset unless mcb for A?C 3,4,5 was switched off. This is the first time this circuit has been a problem. So this has altered the steps:
Turn off MCB for a/c 1 and 2 and DP switch for DW.

1. then see if with the DW circuit on at the labelled DP switch the RCD trips when you turn on the MCB for a/cs 1 and 2?

Turn off MCB for a/c 1 and 2 and DP switch for DW.

2. now turn on MCB for a/cs 1 and 2 and then turn on DW DP switch.

Turn off MCB for a/c 1 and 2 and DP switch for DW.

3. Turn on MCB for a/c 1 and 2 and leave DP switch for DW off for several hours.

What does RCD do for 1, 2 and 3?

Washing machine unplugged. BOTH mcb's off

1. RCD trips if either mcb is turned on, when other one on.

2. MCB a/c 1,2 on, turn on DW DP. RCD trips if other a/c mcb on. Doesnt trip if other mcb off.

3. In process of 3. For about a couple of hours now, no RCD trip but only if mcb 3,4,5 is off. Otherwise trips immediately.

I get that this now makes it even more complicated. Cant seem to get an electrician for a 2-3 weeks.
 
As this has been happening since the A.C. units were fitted, then this has to be the main suspect. What heating did you have before? How was it wired? Has some of the fixed wiring been used for the AC controls? Or are there time switches or thermostats still in situ?
 
Be interesting to get a sensitive clamp meter on each of the aircon cpcs to check leakage. Maybe they need to be on separate RCBOs.
 
Borrowed Neutral maybe??? did the A/C guys leave you any testing results or did they just install switch on an then leave.?
I posted this yesterday and since many people have tried to help, but for some reason you haven't answered what I consider a relevant question, so did the A/C installers do any electrical testing, if so did they leave you any paperwork, certificates of any sort? from what has transpired since I doubt it, but it would be useful to confirm. If the answer is no, then the first step would be to carry out a full set of electrical tests.
 
Last edited:
Hi - the AC compressor units, do they have a local isolation switch next to them? Hopefully they do, if so perhaps try the tests with air con MCB on but the units isolated locally. Isolation switch may look like this ...

IMG_0969.JPG
 
Had similar last year. Erroneous tripping of rcd. No obvious low readings on insulation resistance testing of circuits. Could not narrow down to a specific circuit and no new installs to point the finger at unlike the aircon units. Moved kitchen ring main away from rcd and put it on rcbo and all was ok. My summary was that combined earth leakage of all the kitchen appliances plus that of the downstairs socket took the earth leakage over the edge in certain scenarios.
 

Reply to Strange RCD tripping problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
465
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
374
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
610
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock