Hi,
Looking for a bit of advice . I have a summer house in my garden that has the following setup.
50amp breaker from house consumer unit from this is 18m (3core) armoured cable. This is fixed externally to the house wall and goes underground for approx 2m. Inside the summer house is a consumer unit with
1 x 40A 30mA RCD
2 x MCBs (1 x 6A & 1 x 32A)
The 32a is used for 5 two gang sockets radial installed. The 6a is for an LED light bar.
I’ve been told that the consumer unit in the house should be 32amp and that the breaker for the sockets needs to be on a 20amp breaker as the sockets are radial and not ring - does this sound right ?
Thanks
Paul