A job ive been to has the main gas and water bonded but no supp bonding.
Am i right i saying that you can take your supp bonding in bathroom from the light or switch ??
yes you can take supplimentry bonding from the bathroom light cpc or light switch providing it has a cpc to pipe work etc allthough accoring to the 17th edition if everything in a bathroom is on a rcd and all pipe work in the room has good conterniety between them you do not need to supplementry bond if you need to supplementry bond you should use 4mm cable. what job are you doing in the house because if you havent done anything to do with the bathroom you dont need to worry about it
There is no dual RCD board, only a Main switch side and rcd side. so no rcd protection in the bathroom. Customer is worried it wont pass a test/inspection.
Supplementary bonding and RCD protection on bathroom lighting is not a failure on a PIR.
However, if there is a spare way on the RCD side of the CU then move the upstairs lighting circuit (or whichever circuit bathroom lighting is on) to that .
This then sorts out both probs.
hi there
check weather you water pipe coming into the proerty is plastic if it it there is no need to bond the bathroom RCD protct needed etc all other metal services need to be bonded see 701.415 in the regs book
supplementry bonding is for additional protection provide you have ads automatic disconnection of supply
cheerrs
hi there
cheerrs
i thought that was the case as well but when i spoke to the nic eic i was told that there is no need to bond the water supply if all the pipe work is plastic only :mad:
Reply to Supplementary Bonding.. ??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...